Hi there,
I'm trying to perform a mask move operation in RSlogix 500 using the S2(Status) so that it will be easier to transfer them to our SCADA Platform.
Specifically the Online edits(Main tab) and Processor mode(CHAN 0/1) bits.
The question is : Is this possible? If so, would my source be S2 - Status and the destination B3 - Binary?
Thanks,
AD
"Out beyond ideas of wrongdoing and rightdoing, There is a field. I'll meet you there."
From what I see, the MVM won't work with the S2 data. Since it is only four bits, I would use an XIC for each bit and have each one write to a bit in an integer file.
OG
bst mov/cop/cps s:1 n9:0 nxb and n9:0 15 n9:0 bnd
drbitboy,
You just spoke another language to me sir lol.
Thank You all for the feedback. I guess I will try the MOV and XIC!
What I said was this:
Code:
       ____________
---+--[MOV         ]---+---
   |  [Source   S:1]   |
   |  [[U]Dest    N9:0[/U]]   |
   |   _____________   |
   +--[AND          ]--+
      [SourceA  N9:0]
      [SourceB    15]
      [[U]Dest     N9:0[/U]]
A little cleaner, less clear perhaps, needs a comment e.g. "Cannot use MVM from S register, apparently, so do the same thing with MOV and AND instructions"
Are you sure?
For me, the rung verified with the MVM, but I still had an error in the results saying Invalid Data Type. It was odd. Never seen that before. I still see that when I try it now. That was using the ML1400. When I used a 5/05 everything worked fine. Looks like it works for all 5/01 through 5/05, but none of the ML.
OG
Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
106
I have a little bit of experience with Allen-Bradley. I have a Micrologix 1500 (RSLogix 500) and a PanelView Plus 7 (FactoryTalk View Studio ME)...
198
buen dia. tengo una falla al pasar los tags de mi plc SLC 5 0/4 a mi panel me aparece un error Problem writing value " " to item <tag name>...
97
Will someone please convert this logic to pdf?
142
Hello, Haven't been on in a while. I need to generate a bit level pdf of the I/O for RSLogix 500. I can generate a report but it just shows the...
173