RSLogix Compact Analog Output Control
KI4KKT
Mar 2024
Cullman, AL
I am having trouble with getting no control of my analog output signal. I am using the SCL function block to control my analog output. The logic appears to be working correctly but I am not able to get it to change my analog output. Any assistance will be apricated.
The SCL looks Right. What is it not doing?
32 should be around -1. Are you saying that if you change the Input that the Output just stays the same?
The SCL Output changes from 0 - 5 but the Physical output signal doesn't really change. Most times it stays around 2.384 VDC. I have the device setting set to 0 - 5 V. I'm not sure if the logic is correct or are both of my outputs damaged.
What is the type of Compact output card are you using? Most of those aren't 32 bit cards so they wouldn't accept 0.0 to 5.0 as a output.
If you tell me the exact model of the Analog Output card i can help you alot more.
So to produce a 0 to 5 vdc output configured for "Engineering Units" you need to change the SCL output to 0 to 5000 and double check the Wiring.
Also remove the second output from the SCL instruction. I believe it may be copying REAL (32) bit ---> INT (16) + INT (16)
If you want them to be the same just MOV Channel0 into Channel1 after it has been scaled
That worked. I did not realize that I had my output too small for the resolution. This is my first time creating a scaling function and did not remember about the resolution. The second output was just trial thing. Thank you and to all the others as well for the assistance.
Is it possible to upload a program from a CompactLogix using RSLogix 5000 version 20 and get the descriptions of the tags included? Every time I...
1,900
Hi all, I have 2 Allen-Bradley CompactLogix PLCs (1769-L35E) talking to each other over ethernet. One is producing tags, the other is consuming...
8,889
RSLogix5000 -> File -> Compact What does this do exactly, or do you know of where I can read about it? I can't find reference to it in the help...
9,713
What is the difference between control logix, Soft Logix and Compact Logix ???? iam trying to learn rslogix 5000 myself...i worked on rslogix 500...
21,167
Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
87