RSLogix PIDE SPOper being cleared when changing modes?

daveman

Member
Join Date
Jan 2012
Location
Houston
Posts
1
I have 2 PID loops controlling a valve, the primary one is controlled from flow, and the secondary one is controlled off pressure if the pressure rises above a setpoint.

I have them setup so that the one in control is in Operator Auto and the one not in control is in Program Manual and the active PID's CV is followed. However when I switch from Operator Auto to Program Manual, the PIDE SPOper Value is cleared to zero.

In Program Manual I also cannot adjust SPOper either in the logic or at the HMI. Ideally I want to set SPOper so that whenever the PID enters Program Auto, SPOper is persistent and will be the setpoint used.

I also want to be able to set SPOper when the PID is in Program Manual, as this affects the switchover point. Am I missing something? Thanks
 
welcome to the forum ...

I recommend that you take a look at the FIRST TWO posts of the thread at the following link ...

http://forums.mrplc.com/index.php?showtopic=14562&view=findpost&p=71278

the information there has helped many people with questions similar to yours ... be sure to look at the PDF files which are attached to each post ... if that doesn't help, then I recommend that you post your entire program file here ... we'll be glad to take a look and try to help you nail all of this down ... (you'll have to zip the file before posting - forum rule) ...

good luck with your project ...
 
The part on Multiloop Selection in the document that jamesau suggested is what you want. There is no need to put either of the loops in manual if you set it up this way.
 

Similar Topics

Greetings ... someone sent me a request for some student handsouts that I developed ... turns out that I had this hosted on my business website...
Replies
0
Views
146
Hello im using PIDE in rslogix 5000 - mode is DEPENDENT. im using it to control the temperature, via burners. im having some problems with...
Replies
10
Views
5,126
While troubleshooting control issues due to windup, it would be helpful to be able to view the error term due specifically to the error term in...
Replies
5
Views
1,897
Hi all, Having some issues setting up a PIDE Cascade control loop. Have been trying to go through the Wp008 doc but there's probably something...
Replies
9
Views
5,703
I have an application that I was wondering if these function blocks could help me out. I work at a hydro-dam (less than 4 MWatts), and we control...
Replies
5
Views
2,613
Back
Top Bottom