Rsview32 communication error

frw312

Member
Join Date
Jun 2005
Posts
85
I am trying to get a project to communicate with a PLC5 on DH+ or TCp have tried both. The PC i'm working from can connect to the PLC okay but Rsview32 returns an error "communication driver not configured" I have configured the channel and nodes as they are in another project that works onatherC but not here. I'm sure it is something simple that I'm missing. Any help would be welcome. Thanks
 
What version of RSLinx do you have. LinxLite will not work with RSView32.

If you can, post a screen shot of your channel and node configuration.
 