s7 200 counter reset after one month or year

nouman

Member
Join Date
Jun 2015
Location
rawalpindi
Posts
6
hello i want to know that how i reset a counter value automatically on a specific time(e.g at 2 am)or after month or one year in siemiens s7 200
 
With READ_RTC you can get the current day/month, time etc and then just compare it with your prefered reset day/time.
 