S7-313C communication Error

mdsami849

Member
Join Date
Feb 2008
Location
KARACHI
Posts
2
I m getting an error message "Communication adopter damage" when i tried to connect a S7-313 PLC with PC via MPI cable. Then i take it to a professional and he is getting the same message. Well is anything related to the communication port has problem( some IC or so inside) or what? Can anyone help me regarding the situation;)
 
Do you use the right com-port?

Look under:

'Simatic Manager / Options / Set PC/PG-interface / Properties / Local connection'.

Also:

Check the Transmission-rate: i have a small switch on the side of the PC-adaptor. The two rates must be the same.

Check under: 'Simatic Manager / Options / Set PC/PG-interface / Properties / MPI' if your 'pg/pc is the only master on the bus' because maybe it's not the only master on the bus.
 
Also check you are addressing the correct plc. The 313 plc will have an MPI address. (1 or 2, usually). Set the pg to have a different one( I use 3). My settings "Local connection" settings are: "COM1" and "38,000".
Also check via "Windows" "System settings" that your 9 pin port is "Com1".
I also use a USB-9pin adaptor which gives a "com" address of 4.
 
I m getting an error message "Communication adopter damage" when i tried to connect a S7-313 PLC with PC via MPI cable. Then i take it to a professional and he is getting the same message. Well is anything related to the communication port has problem( some IC or so inside) or what? Can anyone help me regarding the situation;)

First, what cable do you have Serial, usb. You must have the drivers loaded for the adapter you have. Go to your PG/PC interface and select the correct adapter. Once you have selected the correct adapter go to step 7 and select accesible nodes to see if anything shows up. If not go back to the PG/PC interface and modify baud rates until you find the correct one.
Hope this helps.
 

Similar Topics

Dear experts, I have the following setup: CPU-313C (6ES7313-5BF03-0AB0 V2.6) + CP343-1 (6GK7343-1EX30-0XE0 V2.0) communicating with Siemens PC...
Replies
7
Views
2,706
Hi, I have a arrangment of 13nos TP177A HMI , 13 Nos S7-313C CPU's & WINCC 6.2 on MPI network, My problem is wincc communication is break for few...
Replies
4
Views
4,688
Hello, Is there anybody who can help me to communicate with Siemens PLC and OPC Server and observe data in opc client. I have Simantic net +...
Replies
5
Views
2,307
hello, sir , i m having 313c siemens plc with usb adapter , i want to communicate it with wonderware's intouch , will it possible plz advice me,
Replies
2
Views
3,549
hi everyone, I have a S7 313C Cpu communicating with a pro-face touch screen (AGP 3000 Series), the problem is we found out that the cable...
Replies
1
Views
6,610
Back
Top Bottom