Dear Sir,

We have S5 PLC type ET-200U modules. I want to communicate through s7-400 type PLC to S5 ET-200U through profibus.
Is it possible?
The ET module is IM-318B type no : 6ES5-318-8MB11.

I tested with 318-8MB12, it is working.

Is there any body can help?

Regards,
AppaRao
 
Yes, it should be possible.

In the STEP7 hardware catalog the last digit in "6ES5-318-8MB11" is ignored, it says "6ES5-318-8MB1."
So it seems that it makes no difference if it is an -8MB11 or -8MB12.

By the way, this must be an existing application, as the whole ET200U range has been put on the phase-out list.
 
Hi Jesper,

I find a difference in 318-8MB11,-8MB12.
In -8MB11, the DIP switch of 8th is for 'slow speed', where as in -8MB12 the same was meant for 'siemens DP' or 'Normal DP'.It is working with Normal DP mode.

I tried with lower baud rate also. But no use, Is there any other way to check with -8MB11?

Regards,
Apparao
 
I dont have such a system to try, so I cant tell much.

Did the -8MB11 work before ?

Try to experiment with this setting in STEP7 hardware configuration of the module:

[attachment]

et200u.jpg
 

Similar Topics

Greetings, I had an issue with a RIO rack 2 and IFM I/O Link dropping on my network. I would loose connection for a second or 2 then they would...
Replies
3
Views
57
I HAVE B&R POWEL PANEL 400 HMI. THE ISSUE IS HMI NOT BOOTING, DISPLY SHOWING CONTIUESLY (ATTEMPTING TO A BOOT HARD DRIVE....)
Replies
1
Views
60
Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
Replies
0
Views
83
I have a micro1400 processor running two routines (transfer compression/compression molding press). Recipe parameters are stored from job to job...
Replies
0
Views
79
Is there anyone who can help me regarding this HMI is missing the choices when I make a new Device in TIA. Only 7" Display above are the choices...
Replies
3
Views
109
Back
Top Bottom