Siemens 226 CPU and more RS232 ports

sonarbell

Member
Join Date
Mar 2004
Location
Leicester
Posts
28
Simply put..I have a Siemens CPU226 with 2 comms ports. Currently one is used for the HMI and the other for Online programming.
I have a Barcode reader and a labeller to interface to the processor. Both using RS232 comms.. But Siemens dont do an additional 2 port module..

Anyone any ideas as to how to resolve this ??

Thanks in advance.
 
Last edited:
My solution:
Add an ethernet CP 243-1 to your CPU226.
Get from Anybus or other brand, two Gateways serial / ethernet so you can connect the two units to your PLC. You will also be needing a small switch.
 
Thanks for the info..I have opted to use a profibus expander module which will allow me to communicate to the HMI and my laptop. This then allows my 2 comms ports on the CPU to be free for comms to the other pieces of equipment

Thanks again
 

Similar Topics

Its a S7-200 part # 6ES7 216-2BD23-0XB0 A customer sent me one of these to extract the program out of. I have zero experience with Siemens S7...
Replies
5
Views
2,234
hello once again im here asking a beginner question does anyone know how much current does the internal power supply (24v)from the siemens s7...
Replies
4
Views
3,685
Hi; Can anyone please explain me the difference between Siemens PLC CPU226 6ES7 216-2AD22-XB0 and CPU226 6ES7 216-2AD21-XB0?
Replies
3
Views
2,341
Hello guys, i am new on this forum, i need help in programming siemens s7 200 with micromaster 420 that is connected with motor. I know how to...
Replies
7
Views
5,116
We are working on a project where we were able to get rid of an obsolte Festo PLC and replace it with a Siemens S7. Couple of qiestions: 1. We...
Replies
1
Views
2,887
Back
Top Bottom