Siemens CPU928B

Help Please

Member
Join Date
Feb 2010
Location
Decatur
Posts
9
I am looking for communication information for a CPU928B for a S5 135U. There are 2 remote racks with S5 ET100U and there was a computer operator interface station. I need to replace the computer operator station but I cannot find what communication protocols are available.
 
Is the PC connected to the CPU or to a CPXXX like CP524 in the S5-135U rack?
The ET100U should be communicating in Sinec L2-DP now called Profibus-DP
 
Thanks for the link on the manual. I'm not ready to start digging into the finer points of making it communicate. I am just curious as to what the communication protocols are so I can see what HMI options I have that will talk to it. Thanks
 
The bottom port on the CPU would be a TTY port so comms would have been by AS511 protocol over a TTY connectecion. TTY is a current loop interface that would normally have been implemented via an RS232 - TTY convertor.

Nick
 

Similar Topics

Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
3
Views
53
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
Replies
2
Views
75
Hello to all, I'm just starting with using CodeSys. Immediately, I have noticed that Codesys doesn't use data blocks like for example S7 does...
Replies
11
Views
160
Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
10
Views
109
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
329
Back
Top Bottom