Siemens KTP1200 Download Issue

mjp123gp

Member
Join Date
Mar 2012
Location
Savannah, GA
Posts
94
Hello, Hoping you guys could help solve an issue I'm having with a Siemens KTP1200 Basic HMI.

I've been onsite for a few days making changes and haven't had any issues downloading to this HMI, but yesterday it started giving me trouble.

Everything compiles fine and the download starts but when it gets to the part where TIA Portal says "Loading Configuration - File pdata.srt is being loaded", it just stops and eventually the download will fail. When this happens, The screen on the HMI is blank and with text that says Shutting Down but it stays stuck like this until I cycle power to it.

I've tested the file on another HMI here and it downloads fine with no errors. Is there anything I can reset or reload the firmware on the HMI? Could it be corrupt OS or more likely hardware issues? Once I cycle power it comes back up and runs the old application with no issues, it just won't let me download the new file.
 
I just tried that but it didn't work.

I was able to get the download to work by restarting the HMI and putting it in transfer mode.

It still takes a lot longer than it has been in the past but eventually it works. I just did my last download for the day and it took almost 10 minutes to get through the pdata.srt part of the transfer. Its never taken more than 20-30 seconds in the past.

I've been making occasional updates to this HMI for the past 6 months and never had any issues.
 

Similar Topics

I've got TIA portal v18, KTP1200 HMI. I want to add a slider bar (if that's the correct name for it) to an HMI screen. Baslcally, like a...
Replies
8
Views
1,120
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
9
Views
181
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
145
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
304
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
114
Back
Top Bottom