SIEMENS LR460 Radar Level Meter access problem

ypf_108

Member
Join Date
Jul 2009
Location
china
Posts
160
SIEMENS LR460 Radar Level Meter,Set the maximum range 48 m, the minimum range 0 m.I have installed the RSLOGIX 5000 V17.00
The output 4-20ma current signal. 1756-if8 the signal acquisition module, the module uses differential access method, HIGH ENGINEERING 1600, LOW ENGINEERING 0.
I have two questions:
How do I collect the module to the value of 0-1600 converted into the actual value?
Module value is 0-1600, the program on-line, the module channel value is negative, why do it? How to solve? thanks
 
Here's your first hint: There's a button on the bottom of each post that looks like this:

It lets you edit your original post without needing to make 3 different ones like you did here.
 
First, check your wiring, mut comply with attached file.

Second, setup your radar according to your needs, 4 mA=0 meter, 20 mA=16 meters or whatever you measurement is.

Third, config your IF8 according to your needs.
 
bobbias,What do you mean you say it? I am now to find a solution to the problem of the. Understand?
I have already set up 4 mA = 0 meter, 20 mA = 48 meters, but how do I collected the module 4-20MA converted into the actual unit value for the meter do?
IF8 relatively large fluctuations in the data collected ,why?
 
Last edited:
I think he's asking two questions.

1) How is the 4-20mA is converted to 0-1600 in his whatever PLC uses RSLogix 5000 as a development tool.

2) Why the signal appears negative (at the input?) and/or why are there flucutations

I can't help with the first, but for the second, does the level appear stable at the level transmitter, or are the level readings on the radar unit fluctuating, too?
 
danw,danw said right. I still do not check the reading, and 4-20MA current signal. Level meter is used to measure the coal bunker of coal-bit.
If the collection to 1230, then the thickness of coal?
 
Hi ypf_108

I can't help you with your RSLogix but I can with your LR460. Once you've got the device properly connected and configured in your control system, we will need to get reliable readings.
Click on my name and then click the contact info tab and send me a private message with your location in China. I will be able to get someone from our China location to help.
Regards
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
9
Views
182
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
145
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
304
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
114
Hi everyone hope you'll well. Is it possible for me to download a Crack version of tia portal v13..sorry to say this but the software is very...
Replies
5
Views
198
Back
Top Bottom