We have a Siemens S7-400 PLC which is 3 years old running well until today.

The CPU has a EXTF fault and will not go to run.

Attached log file. Appreciate any comments or feedback that might help rectify the problem.
 
The "Memory Reset due to inconsistent data" sounds to me as that the program has been corrupted.
Is there an EPROM ?

There is also the "STOP caused by I/O error".
Could this be because there is a hardware fault ?
Or because the HW Configuration is bad ?

Try to load a program backup onto the CPU.
Also, try to change i/o modules and/or the backplane !
 
this error can also be caused by a bus fault. is there a PROFIBUS or other industrial netwok connected? if yes, check your slaves or bus line. or terminating resistor.
 

Similar Topics

Good day, I need help locating/dowloading PLC Siemens Saphir SIO ACX32 driver for Proface GP-Pro/PBIII. I am in the process of upgrading a...
Replies
0
Views
1,401
Hello Experts, I would like to seek advise on how or what tag i should use or do to get the PLC diagnostic buffer to know what is the root cause...
Replies
14
Views
5,699
Dear Sir, I have a healthy profibus communication between SIEMENS PLC S7 400 and Allen Bradley drive PF700 using 20-comm-p profibus dp module...
Replies
3
Views
2,839
Hi good morning all... First, I want to know what is the role of subroutine program in PLC programmming and type of subroutines how its...
Replies
6
Views
2,114
Hello Everyone, I use PLC S7-400 with Ethernet module CP 443-1 and i want to communicate with My galaxy via DAServer. I configure my PLC with...
Replies
2
Views
3,422
Back
Top Bottom