Siemens SITOP UPS Connection

bgtorque

Member
Join Date
Oct 2013
Location
Northampton
Posts
127
Hi all and Happy New Year. *I have a a Siemens S7-314 CPU and a number of I/O modules. *Powering the PLC is a PS307 120/230V (10A) PSU. *As a fail safe, I also have a SITOP UPS, comprising of:

- SITOP UPS1600 (10A) PSU

-SITOP PSU100S 24V (5A)

- SITOP UPS1100 Battery*



My issue is with connection between the SITOP PSU100S, UPS1600 and the PS307 PSU. *My devices need around 8A, hence the*10A PS307 and UPS1600, but I was told that I could have a reduced size for the*PSU100S, since it is only trickle charging I guess? *Can anyone guide me to a connection diagram that shows the power connections for*these 3 devices? *I've since*talked again to Siemens and they've suggested omitting the PS307 and powering the PSU direct from the PSU100S, but this will not have sufficient current for all of the devices that I was intending to supply.



Thanks.
 

Similar Topics

Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
9
Views
58
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
311
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
163
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
313
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
126
Back
Top Bottom