This is a rephrasing of an earlier thread - which should be deleted - sorry, I'm new new to the forum concept - don't know how to delete an earlier thread!

Please advise if it is acceptable to use the CPU power supply unit PS 307 5A 24VDC/0VDC supply outlets to power a SM322 32xDO 24VDC/0.5A (6ES7 322-BL00-0AA0) module.

I have wired the DO module front connector correctly and connected it to the PS 307 5A in order to observe the LED indication of output status.

There were no lamps or other loads connected to the outputs.

Now, with the module re-established in its industrial setting and connected up to indicator lamps I find there is insufficient power to drive more than 2 lamps whereas last week, before taking the module out, ALL lamps could be simultaneously driven - during Lamp Test for example

Could the module have been damaged by operating it without output load in the form of the indicator lamps?

When I connect certain lamps other LEDs on module glow or pulse dimly even though output is "0" - a possible earth fault?
 
Ok
1st - simply post on the last thread that it has been replaced and copy a link to this one - I'll do that for you shortly -
2nd.
if this is a new card on an existing system then remember the power supply is for the whole system not just that card.
it is common to see more than one supply
a 5A and a 10 or 20 Amp in a panel.
Please give a few more details.
 
Thanks IanT and KalleOlsen for your help.

The cause of the symptoms turns out to be a 0V contact knife being open; hence, presumably, no reference voltage and the strange output characteristics.

On replacing knife contact all is as expected.

So, in reply to my own question, it would appear that using the PS 307 PSU for powering DO module without load for bench test purposes is an acceptable procedure and the module is undamaged - phew!
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
9
Views
256
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
159
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
311
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
124
Hi everyone hope you'll well. Is it possible for me to download a Crack version of tia portal v13..sorry to say this but the software is very...
Replies
5
Views
199
Back
Top Bottom