Siemens Tisoft Counter Maxed Out!

tlrabun

Member
Join Date
Aug 2005
Location
Louisiana
Posts
1
I am using a counter to keep track of engine run hours. The problem is that at 32767 hours, the V memory register maxed out. Is there a solution to continue counting beyond 32767........
 
When I have needed to count above 32767 I use a series of counters. I have a counter that counts up to 10,000. When that counter reaches 10,000 it resets itself and increments a second counter. I then use the TCC values of both counters to give me the total count. If you want time you can do the same thing. Use a one timer to count seconds, when it reaches 60 reset it and have it increment a counter for minutes. When it reaches 60 have it reset and increment a counter for hours. If necessary you can have it increment a day counter. With a couple of counters you can go up 32767 days or about 90 years. I hope your engine test doesn't last that long.
 

Similar Topics

Hi. I have 2 files where I would like to see the ladder logic differences (similar to the Rockwell compare function). I am using TISoft Siemens...
Replies
1
Views
1,284
This may be very simple, but I can't display comments on my TISoft2 ladder logic. Anyone know how?
Replies
1
Views
1,821
Hello, I have a CPU 317-2DP Firmware Version V2.1.8. In TIA Portal only V2.6 is available, and there is no option to upgrade FW. Then I open it...
Replies
2
Views
92
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
9
Views
286
Hi PLC people, think about this scenario: The PLC is somehow connected to the same network with the facilities` network. Then someone connects to...
Replies
2
Views
103
Back
Top Bottom