Strip width measurement on an Edge milling machine

Prince

Member
Join Date
Jun 2002
Posts
284
Newly I am trying to improve an "strip edge milling" machine. as you know better this kind of machine mills the steel strip edges on either side for a better welding result in Pipe making .At the first glance the machine have a mechanical transducer in order to measure strip edges and calculate the width of the strip. I want to change the sensors into no contact type. I checked Siemens and they offer 3RG70561 family. Its range and resolution were acceptable the only problem I've found about it was this small notification in the catalog that their working distance must be 65±1 mm. here I think that I will have ±5mm vibration

2zg5et1.jpg


This Family are Laser sensors so why must their distance to the strip be so important?
Can anybody suggest me another sensor not sensible to vibrations ?
 
Last edited:
I think the specifications are saying that the sensor should be placed at 65 mm nominally. It appears to give a usable output from 45 to 85 mm (a 40 mm range). So its analog output will be at one extreme at 45 mm and at the other extreme at 85 mm.

The sensor will probably work correctly but it will indicate the 5mm variance. You will have to take that into account in your program. You may need to program a suitable filter.
 

Similar Topics

hello all, is anyone aware of sensor devices which may be able to accurately measure width and thickness of a steel strip. i am currently...
Replies
6
Views
4,062
No trivial trains and tunnels this time! This is an actual problem that was solved about 20 years ago by one of our engineers. The goal is to...
Replies
25
Views
6,127
Hello Experts; Good day. I have strip chart OPC version 1.4.1.6. I have RSLOGIX version 13 to 309Studio 5000). I have RSLINK LITE version 4.0...
Replies
0
Views
1,260
Hi, Just wondering what everyone uses for terminal strip labels? We have an old Roland DXY-1150 plotter with ACS (Murrplastik) software that...
Replies
8
Views
2,136
What is a good method to take a floating point number and strip off the numbers to the right of the decimal so they can be use in a compare...
Replies
17
Views
4,445
Back
Top Bottom