Hello and thanks in advance for any assistance

I am working on a project to convert several Symax 600 PLC's to AB, All I have are teh current programs and cannot figure out the I/O addressing scheme of the symax PLC's. Which bits are real I/O and what is internal? Any help would be greatly appreciated.

Regards,

John
 
The Sy/max family used free format addressing. There are no fixed addresses anything such as I/O, internal coils, timer/counter, memory addresses. The only dedicated addresses are the system words which begin with 8001.

I/O and other coils are addressed as the bits (1 to 16, right to left )of any word. Each address also has status bits (17 to 32)

You need to look at the rack addressing of the processor to see which addresses were assigned to real world digital and analog I/O. Addresses were assigned to I/O cards based on the number of words needed by each card. Actual card data is not part of the "program" because the Sy/Max processor did not care what card was or wasn't present (it was up to the programmer to create any error checking using status bits).

For example:
A 16 point digital card would have 1 address: 0001 for I/O 1-1 to 1-16
A 64 point digital card would have 4 addresses: 0002 to 0005 for I/O 2-1 to 2-16, 3-1 to 3-16, 4-1 to 4-16, and 5-1 to 5-16
A 8 channel analog card would have 8 addresses: 6, 7, 8, and 9
A remote I/O communication card might have 512 addresses: 10 to 513

Many of the old Sy/Max manuals can be found at www.squared.com.
 
Thanks

I had been reading the Symax Manuals, but was still a little confused. Guess that's what I get for being used to AB and GE style addressing. Your Post clarified things for me.

Regards,

John M
 
Just remember, the Sy/Max family was introduced around 1980 and they insisted on 100% backward compatibility for the rest of time.
 

Similar Topics

Hello everyone, I m very new with symax.I ma working on one project in which we are adding some i/o cards in one of the remote i/o rack. The...
Replies
9
Views
2,579
Square-D Symax SFI-324 I have used the SFI-510 card for many projects, but I came across a SFI-324. Does anyone have ant tech info on it?
Replies
0
Views
85
I have a few program files that I need to convert into a printable format. We don't have a dot matrix printer available to us. Would anyone be...
Replies
1
Views
746
I have been tasked to upgrade some SquareD PLCs at our plant. I have done several of these upgrades without any issues. However, I have now met my...
Replies
4
Views
2,452
Hello all and thanks in advance for any help on this. I am working with a symax 400 processor and i'm trying to wrap my head around the...
Replies
0
Views
1,024
Back
Top Bottom