Ken Moore
Lifetime Supporting Member
I just looked through my reference manual, I do not see anyway of enabling/disabling loops from ladder. You could always have the loop output going to an intermediate V address, and then use ladder to either pass the loop output to the analog output or some other value.
I have one control valve that has two loops controlling it, one is based on pressure, and one on temperature, depending on the I have each loop output to a V address, then depending on the circumstances, I move the appropriate V to the WY address.
Something like this:
If temp mode AND Not pressure mode, then move temp. loop output to WY100
If pressure mode AND not temp mode, then move press. loop output to WY100.
If you could provide more details on the application, we may be able to offer other possible solutions.
I have one control valve that has two loops controlling it, one is based on pressure, and one on temperature, depending on the I have each loop output to a V address, then depending on the circumstances, I move the appropriate V to the WY address.
Something like this:
If temp mode AND Not pressure mode, then move temp. loop output to WY100
If pressure mode AND not temp mode, then move press. loop output to WY100.
If you could provide more details on the application, we may be able to offer other possible solutions.