I don't run a UL panel shop or do UL designs, but I try to keep my designs UL friendly because several times I've had to have it inspected before installation. Hopefully someone familiar with UL can chime in.
I have an application where I just have a single motor to control with a level switch. Typically, I would put a UL98 disconnect on the panel and then also have a Type E or F combination starter. I do notice that the Type E/F combo starter also offers a rotary handle for access outside of the enclosure.
Would I be in compliance if I used the Motor circuit protector to protect the motor and use the rotary handle as the disconnecting means, or should I have both a UL98 disconnect and the rotary handle?
I would also probably run a 120V transformer or 24VDC power supply for the control circuit.
I'm out of the office so can't quote code but this is a common question we get about our motor starter panels. You can use the MMS is a disconnect if the motor is the only power circuit. For example you could got to a START/STOP button or an HOA using line voltage to pull in a contactor for a motor, but the moment you add a transformer, auxiliary solenoid, or any type of secondary power load, is must use a UL98 disconnect and branch circuit protection for each load.
Using the MMS can be a good cost saver when you can but you wouldn't believe the times I've had to explain why it cost an extra $300 to put a $25 auxiliary load in because of this. Here are two examples of near identical panels using an MMS vs UL98
$645.95 MMS https://www.theautomationstore.com/...-phase-1hp-460vac-460vac-coil-ul-508a-listed/
$968.95 With Transformer https://www.theautomationstore.com/...-phase-1hp-460vac-120vac-coil-ul-508a-listed/
Thank you for the response.
I suppose this makes sense. I didn't think it was legal to use 480V for any controls components any longer.
From what I hear we aren't too far away from requiring ARC flash suits just for 110V panels!
This is an often quoted but not completely true statement. There are a lot of safety reasons to use 24VDC, especially where the control signals leave the enclosure, but it doesn't mean that everything else is illegal.
Arc flash is required for 110VAC.
Question for those panel builders. I'm not a UL shop, but I usually keep my designs UL friendly in case they need to be certified (happens...
1,620
I have (or will be getting) a 250A motor that I am building a starter for. The starter will be in 36x36NEMA enclosure with a disconnect. This...
1,645
Dear, My understanding for Motor control panel for baggage handling system is that it has breakers and protection and PLC, motor starters will be...
3,692
Is this acceptable in the US? I have seen it on machines coming in from Europe, and am curious.
2,821
Could anybody help? Where can I find IEC standard about Electrical control panel ,plc,motor in pdf format? How much does it cost? Thank a lot...
10,047