VFD for Vibratory feeder

To the question: Yes.
Depending on the type of vibratory actuator, you may expect regenerative voltage from the drive motor(s). Because of this the VFD must have a brake chopper and a brake resistor.

But in reality: maybe not.
Depending on the conveyor, it may be designed for a specific frequency, and it may break up if you run it at a different frequency. You have to get acceptance from the manufacturer if intend to run it at varying speeds.
Also, if you intend to vary the transportation speed by the VFD, it may not work like that. If you reduce the frequency, the amplitude may increase so that the material transports at almost the same speed.

A VFD to drive a vibratory conveyor has its use for starting and stopping quickly. Especially stopping quickly can be done with a VFD or specialised DC brake devices.
 

Similar Topics

Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
Replies
3
Views
107
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
Replies
14
Views
242
Customer want to use contactor for their 5HP motor blower application. im leaning to VFD. anyone use contractor for blower application...
Replies
9
Views
212
Hi, I would like to assemble a simulator/practice booster pump system that uses PID to maintain steady water pressure under various outlet demands...
Replies
0
Views
88
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
150
Back
Top Bottom