Quote:
Originally Posted by Ken Moore View Post
The setpoint should be compared to the EU range, which in this case is incorrectly configured. The PID block scales the input PV (0-4095) to Engineering Units, and then calculates the error from Set Point. (Also in EU). The print outs show EU of 0-4095, it should be what ever the input scaling is (assume Type J) then 32-1400F.
Type K is control...