Ignition to Siemens tags
toddp65
Aug 2014
Florence, Ky
282
Hi all
I'm trying to display an indicator on my Ignition HMI and the source is a Siemens memory output. The output is %M0.4 (it's a bool alarm)
I've tried various configurations of the Ignition tags to get Ignition to read the tag from the controller but I'm not having any luck. There are comms because I have other tags reading but they are direct tags such as analog: [BMS Siemens 1200]MREAL36.0.
Ignition 7.9 and Tia Portal ver 15
Can you modify the program to map that boolean onto a DB? It's strange to have that type of memory being used in TIA Portal and I wonder if it blocks external access to those variables.
So i created a new INT tag and then moved a 1 to it from the Bool in the program; I readdressed the Ignition tag to reflect the new Siemens tag and it worked, I just had to reverse contacts to get it to move a 0 when there is no true condition.
PreLC
Yes, that was one of the first variations I tried. I have that document as well. Either way, creating an INT addressing it with 1 or 0 (via a MOV) seemed to work.
do you mean move it to an INT?
No. An INT is a variable type (as is boolean). An M address is an address in memory (which Siemens has consistently told people not to use anymore). A DB is a dedicated address space created by the programmer to hold relevant data tigether.
Think of a DB as the RSLogix500 B,N,F, etc... files.
So you could either look for a DB that had empty space in it (be it a Bool or INT) and map that bit into that space and read it from your Ignition instance.
Looking at Ignition's documentation you actually needed to use MX0.4 to read that bit into Ignition. Did you try that variation?
Wow I completely made the incorrect Flag+boolean->MB connection.
Definitely should be MX0.4, if it still doesn't work, then it's a different issue.
It's been too long since I've used these, but aren't they labelled just M4.0 or something similar in the program? Perhaps that's the way to get them?
The other thing that just dawned on me is that the MB0 byte is at times used for diagnostic or timer, so it may well be overwritten in the program (I assume not, but doesn't hurt to check if that setting is on).
The only other thing I can think of is if TIA protects M bits from being accessible from the outside or if they're stored as the default DB's in the system (which Ignition can't get to unless you disable optimization).
If you can change the PLC program, just map the M bit to a non optimised DB location and be done with it.
No you can access the 'legacy' addresses from outside, also via OPC. I.e. Merker addresses, S5Timers, S5Counters.
It is only discouraged to use the legacy addresses. I only use them for quick-and-dirty program changes..
There are a few system merker bits (Always on, always off, 1st scan, clock bits..) that you can access and which you should only read, but nothings stops you from writing to them.
MX0.4 should work, we use siemens with ignition for most of our projects. Instead of using the ignition siemens driver you should look at enabling OPC UA server on the CPU, this will allow you to use 'optimised db' and browse tags.
Hi all, Got a client who has requested a SCADA system for downtime tracking and so on. Right now, they want to implement it as a standalone...
20
7,803
Someone was recently asking me about an S7-300 driver for Ignition - I can't remember who. The beta is available to anyone - just request access...
2,391
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
118
Hey guys. We've been learning Ignition and going through all the courses on Inductive University. I really like the software and the things you...
20
1,141
Hardware: 5069-L320ERMS2 Software: Logix Designer 35.11 / Ignition 8.1 Issue: When attempting to write to the tag "HMI_DRV200_DynamicTrim" in...
761