I have a small question on the above topic. There are 3 gas detectors in a meter station ( has a Versamax PLC and the program used is View Developer-Quick Panel) whose analog values are being relayed to the gas plant via an analog output module IC200ALG320 (4-20mA) . Now, last week one of the detectors failed and there was no operator in the meter station to look at the alarm and report. The plant E&I guys want to know if they can have a 0-20mA output module instead so they can read the fault codes off those instruments in MS-43. In other words, they would like to be able to see signals < 4mA passed to the output via the software. What are your thoughts on this issue? Is this feasible? can the existing module be programmed (both hardware and software) to produce < 4mA?
You can't do it with the IC200ALG320 (4 channel, 12-bit) module, but you could replace it with an IC200ALG331 (4 channel, 16-bit, isolated analog output), an IC200ALG326 (8 channel, 13-bit), or an IC200ALG328 (12 channel, 13-bit). Any of those can be configured for a 0-20 mA range.
Thanks a lot for the answer. I suppose I will have to make programming changes to the software as well? Right now I am taking the real value (%R) and multiplying it by 320 (The output scale is from 0-32000 = 0-100%. The output is based on counts.) and then converting it to an int value (%AQ) and sending it to the DCS. What chanegs do I need to make in the programming? I think 4 channel output module would be sufficient for now. How would the 12-bit (my current IC200ALG320) to 16-bit (proposed IC200ALG331) make a diff?
With the ALG331, a value of 20000 in the %AQxxx register assigned to a channel gives you a 20 mA output and a value of 4000 gives you 4 mA output. If your program logic puts a value of 2000 in the %AQ address, the module will output 2 mA.
I have attached a screenshot of what I have now with the ALG320 module (4-20mA). here the multiplying factor is 320. how would this rung of logic change to output 0-20mA?
Your image is pretty much unreadable, but if you're currently multiplying a variable that can range between zero and 100 to get a value of 0 to 32000 in the %AQ register, You'll need to change it to:
(Percent * 160) + 4000
That will give you 4 to 20 mA corresponding to zero to 100%, the same as the current setup. To output less than 4 mA, use a "Percent" value less than zero.
any suggestions on which of the modules suggested by you would be best suited to replace my existing module?
The module you're using is limited to 4 - 20 mA range. Any of the three I mentioned are capable of outputting a 0 - 20 mA range.
What are your criteria for making the selection? Cost? Minimum impact on the existing setup? I don't know enough about your system or the constraints you have to operate under to be able to offer anything more than I have already. I've given you three viable alternatives. You know your system better than I. The selection from among those three choices is your call, not mine.
Here's example of impact on the existing system. You have a 4 channel analog module in place. If you replace it with another 4 channel module, then all of your analog outputs can remain at their current address. If you replace the 4 channel module with an 8 channel module, and you have other analog output modules at higher numbered %AQ addresses, then either the existing analog output channels might have to change their addresses or the channels at higher addresses might have to change to accomodate the additional new channels. If the existing 4 channels are the only analog outputs in the system, then this is a non-issue.
As far as cost is concerned, I expect that the ALG320 is the least expensive of the VersaMax analog output modules. I'm sure that the 12 channel, 13-bit module will cost more than the 8 channel, 13-bit module. I'm not sure where the 4 channel 16-bit module fits in the cost structure.
I guess my criteria for selection is minimum impact on the existing setup. and we don't have any other %AQ addresses so adding the 8 channel module shouldn't be a problem, I suppose.
Hi, The VersaMax PLC suddenly stop running (no LED on run function) so I'm trying to upload the program. The HMI connected to it says "Host...
132
Hi, I am trying to set the IP address on the IC200UEM001 Ethernet Option Module. I am following the procedure in the manual for setting a...
429
Hello! Our PLC stopped working.(Controller CPU hardware failure) What can we do? https://prnt.sc/txskqe
1,808
I'm trying to utilize a PLC that my employer already had on hand for a project. For the life of me, I can't figure out how to get my computer and...
5,147
Every time i turn off and turn on the PLC, PLC is not going to RUN mode In the fault table it shows error " system Configuration mismatch" And...
1,753