Several weeks ago I was called to an electrical problem on a
portable 240v 3p 5hp w/auto transformer and controls, Plastic
grinder, found loose terminal in plug. It looked like some of the terminals were tightened and then wires inserted, the grounding terminal was ok.

Here is my main problem. I had to get a 10' ladder to unplug
it from the ceiling. There was NO means of disconnect other
than the contactor at ground level. This really concerned me,
so I locked it out at the buss and red tagged it. Also reported it to Safety Director.

Talked with one of our "master electricians" and he said it was ok.

A few days later they got me a 30 amp fused safety switch.
It is fused 40 amps at the buss. Sence we have several other machines with plugs as the disconnect means I cut the cord about 2' from the contactor panel and put a 3 phase 50 amp plug configuration in line.
Took my lock off and released it to production.

All ok now,,,,,,,,,,,,,,,,,,,,,I don't think so.

About 2 weeks ago someone swapped out this grinder with another one.
Tuesday afternoon the 5 hp motor went out. Day shift found a replacement motor for me to install. When I arrived at the grinder I saw the 10' ladder. So I replaced the motor, installed the same plug configuration. When doing the rotation test, found the grinder open safety switch full of plastic
and not working(stuck closed).

I went to the 2008 NEC and couldn't find what I wanted about means of disconnect for corded portable equipment. It said to look at art. 70E I think. We don't have that.

Could someone look it up and help with this problem.

Sorry about the long rant.

Thanks,

Jeff K.
 
We have a few machines from Europe that don't have disconnects on them, and use plugs. We have multiple "hot sticks" located around the shop that let you shut off bus tap disconnects from the ground without having to use a ladder. Also, any dropped power cords we make sure to keep about 7 feet off the floor so you can walk under them but not have to use a ladder to reach to plug/unplug.

I can't quote you the article, but my boss (master electrician I'm apprenticing under) always told me you are not supposed to disconnect a plug under power. So all the equipment we build have has a disconnect on it we can shut off before unplugging it.
 
Is you question about "cord-and-plug-connected equipment" as a disconnecting means? hint do a google search on the quoted text.

Think about a corded power tool. I don't like the idea of just using a plug even a twist-lock. I have seen this alot in XP location where a disconnect will cost an extra $1,000. Instead they put a XP rated plug and socket connection for $400.
You may want to look up the old line of sight for disconnects and see what is says now. I think there was a revision on it. I don't have the books in the house with me. I design a disconnect means at line of sight same level with out ladders, platforms, etc.

Jeff do you have any of those panel PC any more?
 
If you don't like the plug as a disconnect, and I agree with Jeff, a twist lock is not a disconnect, and is not rated for breaking under load, although the meltric ones I posted are as they hide the arc inside the plug. For 240V 3ph would it not be easier and cheaper to buy a small 3 phase breaker panel and connect anything within sight to it? Use the breakers as the disconnect means and just pigtail plugs out from it?
 
NEC says handle on disconnect means cannot be more than six feet from floor.
EXCEPT overhead bus work - in this case NEC requires a pull stick.

Cord with plug is an allowable DISCONNECT means per NEC
BUT that does not make it safe or acceptible as ON OFF control.

I suppose six foot rule gets a little sticky with a plug at seven feet above floor but it beats bashing your brains out on em.

3 phase relocatable equipment will always pose a rotation problme. Seen lots of outfits fight it. Best solution I have found is have the MASTER phase rotation setup in shop - assemble equipment there - test it there and you should be OK. Use a rotation tester referanced to the shop for testing out in the field.

Dan Bentler
 
Thanks for the interest guys,

Christoff84, We do use those Meltric plugs on some of the
larger (200 amp) equipment. Maybe we should get a quote
on some for these smaller (50 amp) installations.


These grinders are supposed to be "off" when disconnecting
or connecting. Plugs are only for disconnecting means for
maintenance or service. All have contactors, primarily
for the safety circuits.

I sent a link of this thread to our safety director.

Jeff, I do have more of the panel pc's
 
I don't remember what those panels are I just rememeber you had some. Call me sometime
 
Jeff,

Get a copy of NFPA 70e for your personal and for the company's liability protection. If there is an incident, OSHA does not not accept ignorance as an excuse and your life or fellow employee's health are even more important. There are a lot of rules that you may not be aware of. I have a publication authored by Stallcup's and they explain the rules more at a sparkies level so you don't have to try to interpret code verbage.

Definitely a violation of some NEC requirements. I would review:

2008 NEC Article 240 Covers Overcurrent Protection and 240.24(A) Accessability: Disconnect means must be no higher than 79" from floor to top of disconnect. (Not sure if this directly applies)

Article 400 Covers Flex Cord, 400.7 covers Uses Permitted (B) Attachment Plugs has an exception for 368.56 and in 368.56(B)(2) "length ... shall not exceed 6 feet" which also has an exception requiring tension take-up devices, the cord should just not dangle from an overhead receptical.

Meltric may be a good option, check for the suitability as a disconnect under load for an inductive load, just because you can, does that make that the best way to address disconnecting while under load? Arcing usually causes metal to melt.
 

Similar Topics

Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
Replies
1
Views
105
I'm struggling to get an FR-E800SCE to work on CC-Link IE TSN. I'm sure the issue is with the drive, when I plug in the network cable I get no...
Replies
1
Views
103
Hi I have a yaskawa gp7 robot arm which I am going to use for machine tending with a cnc mill. Is it a good idea to buy a SICK laser scanner for...
Replies
5
Views
230
Power flex 527 Network based safety drive had faulty and alarm pop up SOS Code internal fault Unable to set or clear the fault manually or...
Replies
5
Views
112
Loving AB right now... We have an Allen-Bradley 2094-EN02D-M01 Kinetix 6500 servo drive that once had safe-speed monitoring which was eliminated...
Replies
2
Views
129
Back
Top Bottom