FTView ME rev.12 dowloading issue

ceilingwalker

Lifetime Supporting Member
Join Date
Mar 2010
Location
Phoenix, AZ
Posts
1,586
Hello all, I am wanting to upload a new runtime file to my PV+ 1500 and it isn't allowing it because firmware appears to only accept those files created in rev.8 or earlier and I am using v.12. Is this the same as a CPU that requires a flash to a newer version or will this h-ware just not work with the newer s-ware? When I tried to use the transfer utility this is what it displayed:
View alert.PNG
 
When you create the runtime, you can choose to save it as an 8.0 application, see the attached image. This should run in your PV+1500. It should be easier than trying to flash your PanelView to V12, but to answer your question, it is the same as the PLCs in that the runtime file must match the version of the PanelView. Fortunately FactoryTalk View Studio, unlike Studio 5000 where you need multiple versions installed to match the various processors you work with, allows you to save mers in older formats.

ME Runtime Creation.png
 
Last edited:

Similar Topics

Hi All, we've got abnormal experience when configuring Alarm Log Viewer on FTView SE Station Rev. 9.0. We configure columns starts with Date...
Replies
0
Views
1,531
Hi All, we've recently upgraded from FTView SE v10 to v12. Since the upgrade we've been having a problem where the HMI is slow to update tags in...
Replies
0
Views
41
Hi, I have an issue accessing tags in 3 of my plcs'. When I go to select a tag there is no folder drop down as can be seen in the photo. Any...
Replies
0
Views
63
Hello, I have converted RSView 32 to FTView SE 14 (I have tested FTView 12 before as well and there were some difficulties so I moved on to...
Replies
4
Views
185
Hello Experts, I am trying to create a SINE Wave generator and i cannot seem to make it smoother. I have done this before but i forgot the exact...
Replies
6
Views
239
Back
Top Bottom