RSLogix not accepting AOP

cjd1965

Lifetime Supporting Member
Join Date
Apr 2007
Location
UK
Posts
1,659
Hi
So i am working on a old system RSLogix v19.01 and trying to add a spectrum controls 1734sc-IE4CH

I downloaded and installed the EDS and AOP from spectrum website (says from v15 up) and now if i goto RSLogix and install a module there are no spectrum modules in the hardware catalog, only RA devices

So questions

1. Can i verify the installed AOP?
2. Can i refresh the hardware catalog
3. Any other ideas


Thanks
 
Chris,
Have you tried rebooting the computer? There may be a DLL that needs to re-initialize to see the new AOP list.

That's the usual fix for stupid "it should work but doesn't" things.

A

EDIT:
I installed the AOP you mentioned (found here), ran the MPSetup.exe to install the AOP, opened an A2 ACH file (v.19) and had no issues, other than needing to increase the size of the Point I/O chassis to be able to add in the new card.
 
Last edited:

Similar Topics

Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
Replies
1
Views
80
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
2
Views
146
I have a little bit of experience with Allen-Bradley. I have a Micrologix 1500 (RSLogix 500) and a PanelView Plus 7 (FactoryTalk View Studio ME)...
Replies
3
Views
159
I am completely stuck on building a ladder program that requires a start button to be pressed 3 times to turn on motor 1. Then motor 2 starts...
Replies
20
Views
571
Back
Top Bottom