Question about changing Subnet of CompactLogix 1769 and connected Devices

sooner

Member
Join Date
Jun 2021
Location
Kansas City
Posts
5
Hi everyone, I am relatively new to the controls world and I am needing some help on something. We have a pretty new piece of equipment installed here before I started my job. It looks like the vendors who installed the equipment set up the PLC, Flowmeter (Endress Hauser ProMass 100 to be exact) and PowerFlex 525, HMI (PanelView 7) on the wrong subnet and gateway. They left those as the default subnet mask and gateway instead of matching our plant network. The actual IP addresses are fine. So, I am able to communicate to the PLC and equipment, but not without changing some things on my end. I am needing to get everything on the right subnet and I noticed that it looks like on RSLinx Classic, you can simply configure and change the IP settings of all of the equipment, PLC, Flowmeter, VFD, HMI. Is that the right and easiest way to do it? Also, does it matter which piece of equipment I change first? I assume I would need to change the VFD, HMI, and Flowmeter first before I change the PLC.
 
When you make the change, the PLC will lose communications with that specific device until both the PLC and the device have been changed. So, it is up to you what you want to change first. It really doesn't matter. I would leave the HMI for last though. In my mind, it is the least important device.

When it was safe to do so, I would begin by changing the PLC first.

If RSLinx will allow you to change the IP settings, then that is definitely the easiest way to go. Some devices may not allow it.

Keep in mind once you change the IP address, RSLinx will lose the connection to that device.

OG
 

Similar Topics

Does anyone know if there is a way to change the color of the blue text in this picture? I've obviously been playing with the color settings but...
Replies
2
Views
2,161
Hi All, I have difficulty in changing parameters on Allen Bradley VFD 1336 Plus, even I have successfully login in. I appreciate to your help.
Replies
2
Views
2,120
Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
Replies
5
Views
165
Good morning! Let me start by saying, I am still learning about this type of HMI programming. I recently watched a video about recipes and how it...
Replies
0
Views
68
I have some logic that I have written within a 5380 series controller that tracks the time an event is started, while the event is running an RTO...
Replies
2
Views
91
Back
Top Bottom