o_O I am a newbie trying PSIM and am facing difficulty with a counter in the Batch program. I observe that there is significance in the order of the rungs in this case.

Please see this picture

The pump 1 (O:101) trigger flow meter I:105
The pump 2 (O:102) trigger flow meter I:106

Both flow meters are used to increment a counter C1

Pump 1 works till counter = 35, and afterwards pump 2 works

Now when I give counter before inputs (Program 1 in figure) counter is activated by I:105 but not activated by I:106. It just stops at 35.

When I give counter after inputs (Program 2 in figure) counter is activated by I:106 also.

Why?
 
When you stop the pump 1, what ensures that I:105 will be zero thus allowing pulses on I:106 to be seen by the counter?

Either use two separate counters, or edge detection logic for each input to trigger your counter.
 

Similar Topics

Create ladder logic program to count 4 on pulses (not using a counter) and then turn the output on if the on pulse input signal can look like the...
Replies
105
Views
36,183
What ladder logic is required to have an HMI button that gives output when you push it then removes that output when you push it again? For...
Replies
9
Views
3,804
I will apologize in advance for this question. In a PLC scan I understand the inputs are read, then the PLC carries out a scan out the logic and...
Replies
11
Views
4,090
Hello Everyone, I am brand new to PLC's (learned they even existed 3 days ago) and have gone through the tutorial on this site. I am a little...
Replies
4
Views
5,203
Please,: Explain the meaning of Scan cycle in a PLC when it is running a program?
Replies
2
Views
3,199
Back
Top Bottom