SLC 5/03 firmware

Lukas01

Member
Join Date
May 2014
Location
Zagreb
Posts
11
Hi,


I have 1747-L532E (OS302 C FRN 11) and RSLOGIX 500 ver 8.40. In RSLogix I can only choose FRN 10 for processor type. How to upgrade firmware version of CPU in RS Logix 500?


Also, is it problem if I download FRN 10 from RSLogix to CPU with FRN 11?


Thanks
 
Last edited:
I am running version 9.00.00 [CPR9], but you should see the same thing as the image attached. The option is "Series C FRN 10 and later", meaning you should be able to use this choice with your processor with no issue.

ProcType.PNG
 
I am running version 9.00.00 [CPR9], but you should see the same thing as the image attached. The option is "Series C FRN 10 and later", meaning you should be able to use this choice with your processor with no issue.


Thank you for your feedback.


But when I compile my software, a get a warning for channel 0 (I am using this channel for MODBUS communication with 3rd party device).

Warning.JPG
 
Thank you for your feedback.


But when I compile my software, a get a warning for channel 0 (I am using this channel for MODBUS communication with 3rd party device).

The software does not know what firmware you actually have installed, just that it is 10 or higher. It is warning you that in the case you have a processor that is not v11 or higher (ie you have a v10), your channel configuration is not compatible.

Since you do have a v11 firmware, the warning should not concern you.
 
The software does not know what firmware you actually have installed, just that it is 10 or higher. It is warning you that in the case you have a processor that is not v11 or higher (ie you have a v10), your channel configuration is not compatible.

Since you do have a v11 firmware, the warning should not concern you.


Thank you for clarification!


Best regards
 

Similar Topics

Hi, I have just flashed an SLC5/05 Cat No. 1747-L551 FRN8 with the latest available firmware from Rockwell using ControlFlash and now the CPU is...
Replies
4
Views
1,751
Dear All, I need to upload program from slc 500 fixed controller (1747-L40C), series "B" and FRN "6"and to download the program to another PLC...
Replies
23
Views
7,250
Can this be read on RSLogix 500 when online? I don't see it under controller properties. The sticker on the CPU side says "1747-L552 ser C FRN 5"...
Replies
6
Views
3,385
Hello all! I am trying to upgrade the firmware on a 1747-L553. I can get it back to factory. But I can't get my computer to talk to it over the...
Replies
16
Views
3,977
Hi All, I have a customer that is using a SLC 504 processor. The Catalog Number based on the RSL program I have is a 1747-L532C. The OS is a...
Replies
5
Views
2,504
Back
Top Bottom