Old October 20th, 2021, 09:43 PM   #16
TWS
Member
United States

TWS is offline
 
Join Date: Nov 2007
Location: virginia
Posts: 310
Was the system working properly before the radio upgrade?
On your DF1 data capture, I do not see any reads or writes.
Was the system working with the Prosoft module and the L-81 processor before the radio upgrade?
I am suspicious of the Prosoft module configuration.
  Reply With Quote
Old October 20th, 2021, 11:06 PM   #17
PreLC
Member
United States

PreLC is offline
 
PreLC's Avatar
 
Join Date: Apr 2019
Location: Mars
Posts: 397
I wish I knew something about the subject matter of using radio comm, but have you tried using OPC connections?

You can try putting a local LTE based NUC-type device in your control panel, and have kepware running on it.
Then centrally have a Kepware installation on a main server to go online. Also, if you need to troubleshoot PLCs, you can install the software needed on these NUCs and RDP into them to go online?

Not sure if LTE works for your application considering you have rough terrain, but sometimes the sustenance of old tech after the original tech creators at companies like GE have left, it becomes hard to get fully functioning technology.

Found a Kepware page with some actual info too:https://www.kepware.com/en-us/produc...n-bradley-df1/

Also, if LTE is just not an option, maybe something like a WAN connection through tools like Ubiquity's offerings? You can try setting up modern radio tech to get a LAN connection?: https://www.ui.com/products/#default

Regards,
-PreLC
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC.

Last edited by PreLC; October 20th, 2021 at 11:19 PM.
  Reply With Quote
Old October 21st, 2021, 03:14 PM   #18
Firejo
Member
United States

Firejo is offline
 
Firejo's Avatar
 
Join Date: Jun 2008
Location: Redmond, WA
Posts: 1,495
The other thing worth mentioning is if you haven’t already, make sure that the master radio is connected to a good managed switch. With the limited bandwidth you want to limit the traffic that can get to the master radio. It should only be traffic that is meant for the remote PLCs. This needs to include broadcast packets especially if the network is also used for internet traffic. You might have a scenario where the radios are spending all of their resources dealing with traffic not meant for the remote PLCs leaving little to no resources to deal with the actual data exchange that needs to take place.
__________________
Go Hawks!!!
  Reply With Quote
Old October 21st, 2021, 03:54 PM   #19
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 1,251
Firejo
Yea, that was part of the VLAN design but I am going to shark the port to make sure that's what's really happening

TWS
New radios have had this problem since install. DF1 is "supported" but not like the older SD and iNET with the built in ENI support. This is going to be timing based serial DF1 comms with the 5 conversation handshake.

PreLC
I need to work with the serial DF1. I have Ethernet Radio at each location that works fine but the existing equipment I need to talk to is too old.
  Reply With Quote
Old October 21st, 2021, 06:27 PM   #20
PreLC
Member
United States

PreLC is offline
 
PreLC's Avatar
 
Join Date: Apr 2019
Location: Mars
Posts: 397
Quote:
PreLC
I need to work with the serial DF1. I have Ethernet Radio at each location that works fine but the existing equipment I need to talk to is too old.
Well, that makes sense, but might be a good solution to get from DF1->OPC-UA->OPC-UA->DF1, and the same for the communication on the other side.

They already have DF1->OPC-UA connectors. Might be a viable backup, considering PCs and accessories are cheaper.
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC.

Last edited by PreLC; October 21st, 2021 at 06:42 PM.
  Reply With Quote
Old October 21st, 2021, 07:24 PM   #21
TWS
Member
United States

TWS is offline
 
Join Date: Nov 2007
Location: virginia
Posts: 310
Quote: "I have one location that has both Ethernet and a KE module. If I use the ethernet channel it works 100% of the time"
You could try some of these: https://www.rtautomation.com/product/460ecdfm/.
  Reply With Quote
Old October 22nd, 2021, 07:27 PM   #22
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 1,280
Quote:
Originally Posted by Firejo View Post
The other thing worth mentioning is if you havenít already, make sure that the master radio is connected to a good managed switch. With the limited bandwidth you want to limit the traffic that can get to the master radio. It should only be traffic that is meant for the remote PLCs. This needs to include broadcast packets especially if the network is also used for internet traffic. You might have a scenario where the radios are spending all of their resources dealing with traffic not meant for the remote PLCs leaving little to no resources to deal with the actual data exchange that needs to take place.
This is precisely why I always recommend people use Layer 3 routing mode on their radios if they support them rather than layer 2 is easier without planning your network first so a lot of people fall into the trap of using it. Most modern ethernet radios do support L3, so plan out the network (/27 subnet size is plenty for most systems). It makes it a lot easier to manage traffic. On some systems I I've use firewall features to block anything other then the required protocols as well, as a backup.
  Reply With Quote
Old October 23rd, 2021, 04:34 PM   #23
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 1,251
I am using L3 routing for the radios and the traffic to the Ethernet remotes work fine. At 200mhz there is not much room for a GUI but SSH works fine as well as the PLC polling.

The radios themselves stay connected, its only when the DF1 Hdx M/S protocol in involved does my day get worse. Those well timed 5 handshakes that this protocol requires combined with the low bandwidth frequency are just not well tolerated. At least that's how it looks.

and yes I could add a variety of gateway devices at each location to move this communication to the ethernet channel but that gets far too expensive for this application.

In my final act at the end of the week I put serial and ethernet protocol analyzers running on the input and output of the Prosoft DF1 interface to the radio's com port and I saw that the Prosoft would not always respond to the ethernet commands.... That's unexpected. Gives me a little hope that maybe the Prosoft module is the real issue or at least contributing. I need to look at this in more detail next week.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
GE "Intellegent Platforms" no more RIP.. RussB LIVE PLC Questions And Answers 0 November 4th, 2015 10:16 AM
Twido plc to GE mds4710 radio RS232 jechlu LIVE PLC Questions And Answers 2 May 10th, 2010 03:48 PM
GE Micro vs AB MicroLogix 1000,1500 alia176 LIVE PLC Questions And Answers 9 March 19th, 2010 10:06 AM
GE PAC RX3i CMM-004 nogo with 5-wire radio I is a noob LIVE PLC Questions And Answers 3 February 17th, 2010 10:15 AM
How to configure GE MDS4710A point to point Radio Communication wilsonzhu LIVE PLC Questions And Answers 4 June 17th, 2008 06:05 PM


All times are GMT -4. The time now is 07:15 PM.


.