Old October 21st, 2021, 05:25 PM   #1
nmk34
Member
United States

nmk34 is offline
 
Join Date: Apr 2019
Location: texas
Posts: 43
DataStore Plus PanelView plus 700

i need help in getting Datastor plus to create the log file in the location as configure the activex object.
i have an existing project that i want to add datastore plus to it. the global connection is been used by this project to switch displays depending on the status in the PLC program. no macros in the existing project.
i created a new screen and added the datastore activex object.

general tab: on top selected
connection tab:
location of file: "\windows\logs\filename.csv"
trigger: plc_tag1
handshack:???
added some tags also
display setting: location is set off the visible area of the HMI display at run time.

WHAT IS MISSING? MACROS? I do not want to put anything in the global connection,
the runtime project does not create a log file: filename.csv
  Reply With Quote
Old October 21st, 2021, 07:05 PM   #2
janner_10
Lifetime Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 1,208
Step by step guide here:

https://theautomationblog.com/datast...lk-viewstudio/
  Reply With Quote
Old October 21st, 2021, 07:22 PM   #3
nmk34
Member
United States

nmk34 is offline
 
Join Date: Apr 2019
Location: texas
Posts: 43
Datastore plus

I have already run thru this website few times. he is using the global object to change between the Datastore and other displays using macros. my existing project matches his steps with the exception of the macros that changes the display number in the global object. i can not change the global object current tag. i am hopping some one could see if i am missing a step or it can not be done without changing the global object
  Reply With Quote
Old October 22nd, 2021, 09:05 AM   #4
celichi
Lifetime Supporting Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 317
I implement Data Stor Plus by using a hidden screen that is positioned outside of the display window, it has the Dat Stor Active X. I do not use Global Objects.

This screen is opened first, and then followed by my real main startup screen. So in my startup list, I have two screens, one called "ActiveX" (operator can not see) and "Main"

I have also seen applications, where the Active X object is in the screen Header which is a global object, so it is always active.

The screen has to stay open for the ActiveX to function.
  Reply With Quote
Old October 22nd, 2021, 11:27 AM   #5
nmk34
Member
United States

nmk34 is offline
 
Join Date: Apr 2019
Location: texas
Posts: 43
DataStore Plus in panelview plus 700

the runtime file is not created due to error:
Multipple displays in startup. i had tow displays:

datastoredisplay
Main
see below pasted error:

WARNING: To open or convert the runtime application in FactoryTalk View version 9.0 or earlier, install patch. See Rockwell Automation Knowledgebase Answer ID 1041447.
ERROR: Unsupported feature=Multiple Initial Graphic Displays; Component type=Startup
Validation completed with errors. The runtime application has NOT been created.
  Reply With Quote
Old October 22nd, 2021, 11:55 AM   #6
celichi
Lifetime Supporting Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 317
Quote:
Originally Posted by nmk34 View Post
the runtime file is not created due to error:
Multipple displays in startup. i had tow displays:

datastoredisplay
Main
see below pasted error:

WARNING: To open or convert the runtime application in FactoryTalk View version 9.0 or earlier, install patch. See Rockwell Automation Knowledgebase Answer ID 1041447.
ERROR: Unsupported feature=Multiple Initial Graphic Displays; Component type=Startup
Validation completed with errors. The runtime application has NOT been created.
Okay, I am using version 12.

From what I have read, V9 should be able to open 5 displays.

What version are you running?

Have you applied any Roll-Up patches to your PC? If not, I would highly recommend the Roll-Up patches.

I remember using the Screen Start-up macro to write a value to open the second screen (main), prior to v9. Using the Global connections.

Active X screen startup macro writes Main Screen #, Main screen startup macro puts global connection back to 0

I am just not sure how that will work in your application, as you have said the PLC is controlling the Screens?
Attached Images
File Type: png aactive-x.png (18.0 KB, 17 views)
  Reply With Quote
Old October 22nd, 2021, 07:00 PM   #7
nmk34
Member
United States

nmk34 is offline
 
Join Date: Apr 2019
Location: texas
Posts: 43
DataStore for panelview Plus 700

Thank you for your help, i have not applied any patches. i am running ver 11.0
I managed to get the DataStore to work, by adding a button to the Main screen to navigate to the Datastore display which i set to be "On Top". I added buttons to allow me to go back to Main display. I assigned a password to the Datastore display to avoid others from tampering with it. The .csv file was created and logging. probably, the draw back to this method is when the HMI project, loaded after power recycled, the DataStore display needs to run as i mentioned above to start logging. Defiantly, i will install ver 12 and all patches as you described.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Troubleshooting on-site... .pvb file, versus .mer file (Panelview Plus 700) AutomationTechBrian LIVE PLC Questions And Answers 29 February 1st, 2019 12:35 PM
One PanelView Plus 700 with two PLCs? KingPresident LIVE PLC Questions And Answers 5 November 27th, 2018 06:13 PM
Needing some help with conversion from PV600 to PanelView Plus 700... jmobley LIVE PLC Questions And Answers 12 February 21st, 2015 10:19 PM
Issues Upgrading to Panelview Plus 6 700 DAnderson LIVE PLC Questions And Answers 1 July 11th, 2012 03:00 PM
Loading Panelview Plus 700 showshocka LIVE PLC Questions And Answers 18 April 25th, 2012 04:43 PM


All times are GMT -4. The time now is 07:32 PM.


.