Drive 30W solenoid valve with 24V DC 1756-OB16 output card

Hi Experts!

I'm trying to control a solenoid valve (don't have part number, but I've been told its a 24V DC 30 watt coil) with a PLC output card.

Supplier says to use a SSR interposing relay but customer prefers not to. I don't really have room in the cabinet either. Not fond of going against the equipment suppliers recommendation, but while they may not be the most sophisticated (no part numbers), they clearly have experience.

I'm looking for your comments on the feasibility and reliability of not using an interposing relay, and instead connecting the solenoid (via a fuse) to the output card directly. I'm thinking of using a 1756-OB16D output card. It is rated for 2A continuous (subject to maximum card of 8A) and 4A surge.

It also indicates its Pilot Duty (DC-13SQ) of 2A. Can someone enlighten me on what DC-13SQ means? (would my 30W coil require a rating of (30/24 = 1.25A?)

From my limited understanding, the greatest load is at initial energization, 4A at 24V is 96W. This should accommodate a 30 watt coil? I don't know if 30 watts is the maximum, or the continuous power consumption...

The other very important consideration is the inductive nature of the load, and its behavior on de energizing the solenoid. Luckily the OB16 card has the diode from RTN to OUT to provide a source for the current and limit the voltage.

Thanks for any feedback you give!

Cheers,
  Reply With Quote
Old July 30th, 2021, 05:27 PM   #2
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 879
How often is it going to be fired? My preference would be to use a SSR as suggested, and put another diode in parallel with the solenoid to protect that too. They also make DIN connectors with surge suppression built-in.

Surely you can squeeze in a terminal-block sized SSR somewhere? Add another DIN rail to the side of the enclosure or behind the door if need be...
  Reply With Quote
Old July 30th, 2021, 05:48 PM   #3
jetwax
Lifetime Supporting Member
Canada

jetwax is offline
 
Join Date: Jul 2005
Location: Vancouver
Posts: 11
Thanks Rupej,

I expect it will be fired once a minute.

Any comments on the inrush current of a 30W coil? (DC).?

Any insight on the DC-13SQ raiting, and how to interpret?

Thanks for your response!
  Reply With Quote
Old July 30th, 2021, 08:26 PM   #4
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 3,216
Gotta check with the solenoid vendor.

ASCO is tricky, a global statement the DC draws no inrush current, and then in a separate section, explaining that the Next Generation coil (now 15 years old) does draw inrush current:






  Reply With Quote
Old July 30th, 2021, 09:22 PM   #5
JeremyM
Lifetime Supporting Member
United States

JeremyM is offline
 
Join Date: May 2014
Location: Dallas, Texas
Posts: 586
I tend to isolate all but the smallest inductive loads with interposing relays.
  Reply With Quote
Old July 31st, 2021, 05:41 AM   #6
nehpets
Member
Wales

nehpets is offline
 
nehpets's Avatar
 
Join Date: Mar 2009
Location: Wales
Posts: 478
Just point out the cost and inconvenience of replacing an output card compared to a small plug in SSR, they will soon change their minds
__________________
Why do programmers get confused between Halloween and Christmas - OCT31 = DEC25
  Reply With Quote
Old July 31st, 2021, 05:46 AM   #7
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 658
The problem with DC coils is on disconnection, the energy is released with a reverse polarity voltage peak to that of the supply.

The peak suppressor diode is better to place it on the same coil, this way prevents it to circulate through the wiring and induce noise on other nearby cables.
__________________
Suppanel HMI
  Reply With Quote
Old July 31st, 2021, 09:14 AM   #8
L33er
Member
United States

L33er is offline
 
L33er's Avatar
 
Join Date: Feb 2021
Location: North
Posts: 21
ASCO statement is correct. What they are saying their 'Next Generation' coil included a Peak-Hold circuitry that peak higher to open the valve and holding it open at lower amp. Similar to fuel injectors in your car that use Peak-Hold driver.
  Reply With Quote
Old July 31st, 2021, 02:06 PM   #9
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 14,909
I agree with Ife.
It is not the inrush current that is the problem.
It is the inductive load due to it being a coil that is the problem. This causes much more energy to be released in the switching device before the coil when it de-activates the coil.
One can mitigate this with surge suppressors, but better is to use an SSR or a contactor to switch the coil.
__________________
Jesper
See my profile interests for Q&A
  Reply With Quote
Old July 31st, 2021, 02:28 PM   #10
pturmel
Member
United States

pturmel is offline
 
Join Date: Jul 2021
Location: Atlanta
Posts: 91
Using a contactor or SSR doesn't solve the de-activation spike, it just moves it to another point.


I'd use the output card directly in this case, as long as there aren't other high-load consumers, too. (The card has per-point specs and per-group specs.)


No matter what you use, the coil needs spike suppression somewhere.
  Reply With Quote
Old August 1st, 2021, 01:56 PM   #11
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 879
Quote:
Originally Posted by pturmel View Post
Using a contactor or SSR doesn't solve the de-activation spike, it just moves it to another point.
For sure- but it could be moved to a much more robust and cheap+easy to replace point. That's the argument for adding an additional SSR.
  Reply With Quote
Old August 1st, 2021, 05:15 PM   #12
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,712
Quote:
Originally Posted by pturmel View Post
(The card has per-point specs and per-group specs.)

True.

Current per point max:
2 A @ 30 C (86 F) linear derating
1 A @ 60 C (140 F) linear derating

Current per module max:
8 A @ 30 C (86 F) linear derating
4 A @ 60 C (140 F) linear derating
__________________
  Reply With Quote
Old August 2nd, 2021, 01:48 PM   #13
Jim3846
Member
United States

Jim3846 is offline
 
Join Date: Dec 2019
Location: Cincinnati OH
Posts: 213
If your worried about blowing an IO point, why not just change the terminal strip TB to a fused terminal?

Select a fuse that will blow before the IO point on card. Its only a few cents more but will save you a card replacement+ time.
  Reply With Quote
Old August 2nd, 2021, 02:22 PM   #14
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 6,164
You can buy a lot of SSR's for the cost of an output card. Not to mention you can replace a plug-in-style relay without stopping the system. And if you pick the right style panel space isn't much of a factor.
https://www.phoenixcontact.com/onlin...7-80ac975b67c5
  Reply With Quote
Old August 3rd, 2021, 11:28 AM   #15
jetwax
Lifetime Supporting Member
Canada

jetwax is offline
 
Join Date: Jul 2005
Location: Vancouver
Posts: 11
Thanks all for your replies!

The consensus seems to be to use a SSR as an interposing relay. And a Diode.
The problem with this approach is one also needs to add the diode between ground and the output, connected 'backwards' (on the output side of the SSR) to protect against the de energization current that occurs when turning off the solenoid with inductance causes high voltages in an attempt to limit the dI/dT
Does any one know of a SSR with the diode integrated? From my looking through phoenix, AB, and weidmuller I don't see one. Maybe I'm not looking closely enough.

Thanks Tom Jenkins for your suggestion, but the ones I see on phoenix contact that have the free wheeling diode are still only rated for 1A inductive, DC 13. The similar, but less than, the 1756-OB16D card...

I get the idea of it being simpler to just change a relay vs. changing the card, but the cost of the card vs. the cost of the relay is very small in comparison to the cost of a failure in the first place. I'd rather it not fail, and accomplish this with the fewest components.

Last edited by jetwax; August 3rd, 2021 at 11:39 AM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Analog signal and DC Drive issue NBJamie99 LIVE PLC Questions And Answers 8 July 14th, 2008 12:55 AM
Step5 output card fault rob28 LIVE PLC Questions And Answers 3 February 21st, 2006 10:22 AM
DC drive card - OT paraffin power LIVE PLC Questions And Answers 6 October 22nd, 2004 10:54 AM
Automax DC drive Card Configuration. dao LIVE PLC Questions And Answers 6 December 2nd, 2003 07:45 AM
Servo Positioning - AB - HSCE / NO4V Ramil LIVE PLC Questions And Answers 2 June 18th, 2003 08:27 AM


All times are GMT -4. The time now is 05:48 PM.


.