HMI Fractions?
UncleHairball
Nov 2019
Califurnia
I have an existing piece of equipment, using an Allen-Bradly Panelview 5500 running a View Designer program, that requires operators to enter measurements taken with a tape measure. We have lots of problems with users not being able to quickly convert fractions to decimal, so I am trying to change my numeric entries to be fractional instead of decimal.
Is this possible? Can you suggest resources for me?
Thanks in advance for your suggestions.
Metric Tape measures available at Home Depot/Lowes
Have your operators either enter CM or MM directly from tape measure
Good idea, but I fear that adding a new measurement system will make things even more difficult. If arithmetic is not a strong subject, a new unit system is probably going to make things worse.
Thanks for the suggestion, though.
We have similar issues on our equipment, i.e. operators not able to think in decimal. On a new machine we built, they take measurements with a ruler graduated in 16ths and enter them in the HMI during setup. Decimal entry was not an option so I had to figure out the best way to enter fractions.
I ended up storing the value as a whole number representing 16ths of an inch, so for example 3-1/4" would be stored as 52. The arrow buttons simply increment or decrement the value by 1 (1/16"). In the PLC it's easy, just multiply the value by 0.0625 to get decimal inches. The field on the HMI displays a text string which is determined by the following code:
Code:
int q := value / 16;   // quotient
int r := value % 16;   // remainder
cstring result;
if(q==0 && r==0) result := "0";
if(q>0){
    result := IntToText(q,10,1);
    if(r>0) result += "-";
switch(r){
    case 0: break;
    case 1: result += "1/16"; break;
    case 2: result += "1/8"; break;
    case 3: result += "3/16"; break;
    case 4: result += "1/4"; break;
    case 5: result += "5/16"; break;
    case 6: result += "3/8"; break;
    case 7: result += "7/16"; break;
    case 8: result += "1/2"; break;
    case 9: result += "9/16"; break;
    case 10: result += "5/8"; break;
    case 11: result += "11/16"; break;
    case 12: result += "3/4"; break;
    case 13: result += "13/16"; break;
    case 14: result += "7/8"; break;
    case 15: result += "15/16"; break;
return result;
This was done on a Red Lion G3 but I would assume it could be translated to a PV. In our case the entries were always 4" or less so it was reasonable to use the arrow buttons for entry. In the case of a larger range you could probably split it up and use a numeric entry field for the whole part of the fraction.
Code:
cstring result;
if(q>0){
switch(r){
    case 0: break;
 return result;
Now you've really got me thinking. I appreciate your helpfulness very much.
Does anyone happen to know how to install the graphic picture in HMI when I go into blower selection there are no graphics shown not only blower...
51
Does anyone happen to know how to install the graphic picture in HMI when I go into blower selection there are no graphics show not only blower...
77
Hello All, I've been tasked with automating a flatbed press that runs with some pretty extreme temperatures. I've been told it can run close to...
144
Good morning! Let me start by saying, I am still learning about this type of HMI programming. I recently watched a video about recipes and how it...
56
hi everyone, i have problem regarding Audit in FTV ver 12,In audit message "service disruption:<HMI server name>:<SERVICE NAME>" message logged,i...
32
