Kindly, how can we keep the safety ensured on safety doors at high speeds, without stopping the machine at low speeds (if a door is opened).
Our customer needs to run at low speed (with doors opened and alarm horn on), so he can do some operation settings. Of course, to enable the run at high speeds, the doors should be closed.
We are using a safety switch installed on each door, and the switch contacts are wired to a safety relay (double circuit).
So, it is not clear how to enable or disable the safety doors, depending on machine speed, without endangering the safety.
Thank you
__________________

"character may be manifested in the great moments, but it is made in the small ones"
  Reply With Quote
Old May 4th, 2021, 03:40 AM   #2
alan_505
Lifetime Supporting Member
Australia

alan_505 is offline
 
Join Date: Feb 2007
Location: Melbourne,Victoria,Australia
Posts: 676
You will need a safety device to monitor speed, if the speed is at an acceptable value disable the safety door, I think you will need some form of programmable safety controller.


Alan
  Reply With Quote
Old May 4th, 2021, 03:53 AM   #3
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 14,736
If you are changing speeds by using a VFD, then the VFD must support the safety function SLS (safe low speed).
__________________
Jesper
See my profile interests for Q&A

Last edited by JesperMP; May 4th, 2021 at 03:57 AM. Reason: "low" not "slow"
  Reply With Quote
Old May 4th, 2021, 08:24 AM   #4
dogleg43
Member
United States

dogleg43 is offline
 
Join Date: Dec 2005
Location: Indiana
Posts: 464
Several manufacturers make safety interlock switches with an internal solenoid used to keep a door/gate locked. Check with AB or Telemecanique.

I am curious how it is deemed safe to enter the workspace at low speed. Are there any pinch points or rotating things then....?
  Reply With Quote
Old May 4th, 2021, 08:52 AM   #5
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 14,736
Quote:
Originally Posted by dogleg43 View Post
I am curious how it is deemed safe to enter the workspace at low speed. Are there any pinch points or rotating things then....?
This is a relatively recent method that has become popular with VFD control, especially in robot cells. There is usually also a mobile hand operated release button that has to be pressed when the drive is to operate at the slow speed with the door open.
The button is made so that it has to be pressed in a half-depressed position. If you release the button or press the button fully, the drive must stop.
With that and the slow speed, if you feel that you are about to be pinched you let go of the button and the drive will stop before harm is done.
edit: And the speed must be so low that you cannot be harmed by impact alone.

All of this shall be carefully considered in the risk assessment.
__________________
Jesper
See my profile interests for Q&A
  Reply With Quote
Old May 4th, 2021, 11:38 AM   #6
Manglemender
Member
United Kingdom

Manglemender is offline
 
Join Date: Jul 2007
Location: Lancashire
Posts: 1,198
Safe Slow Speed most easily done in a drive but can also be done with a speed monitoring safety relay such as Pilz Safe speed monitor PNOZ s30.

Some advice: Ask for a copy of the signed Risk Assessment which indicates that it is safe to open the guards below speed X.

Nick
  Reply With Quote
Old May 4th, 2021, 12:58 PM   #7
dogleg43
Member
United States

dogleg43 is offline
 
Join Date: Dec 2005
Location: Indiana
Posts: 464
Quote:
Originally Posted by JesperMP View Post
This is a relatively recent method that has become popular with VFD control, especially in robot cells. There is usually also a mobile hand operated release button that has to be pressed when the drive is to operate at the slow speed with the door open.
The button is made so that it has to be pressed in a half-depressed position. If you release the button or press the button fully, the drive must stop.
With that and the slow speed, if you feel that you are about to be pinched you let go of the button and the drive will stop before harm is done.
edit: And the speed must be so low that you cannot be harmed by impact alone.

All of this shall be carefully considered in the risk assessment.
Ok, right, kind of like going into a robot cell holding a dead man’s switch. Thanks.
  Reply With Quote
Old May 5th, 2021, 09:00 AM   #8
LadderLogic
Member
United States

LadderLogic is offline
 
LadderLogic's Avatar
 
Join Date: Jun 2003
Location: Chicagolandia
Posts: 1,397
Quote:
Originally Posted by JesperMP View Post
The button is made so that it has to be pressed in a half-depressed position. If you release the button or press the button fully, the drive must stop.
Yes, this device is usually called "enabling switch" or, more expressively, "dead man's switch". To comply with the safety standards, it should be dual-channel with force-guided contacts.
__________________
Don't trust, don't fear, don't beg...
  Reply With Quote
Old May 5th, 2021, 09:14 AM   #9
mk42
Lifetime Supporting Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 2,710
Quote:
Originally Posted by LadderLogic View Post
Yes, this device is usually called "enabling switch" or, more expressively, "dead man's switch". To comply with the safety standards, it should be dual-channel with force-guided contacts.

I've heard "live man switch" and "3 position enable switch" as well.
  Reply With Quote
Old May 5th, 2021, 11:12 AM   #10
dogleg43
Member
United States

dogleg43 is offline
 
Join Date: Dec 2005
Location: Indiana
Posts: 464
Awww, evidently “deadman’s switch” isn’t appropriate any longer. From a 2011 article.
https://machinerysafety101.com/2011/...-term-deadman/

“Do you use the phrase ‘deadman’ or ‘deadman switch’ when talking about safety-related controls on your machinery? I often run into this when I’m working with clients who use the terms to refer to ‘enabling devices’ – you know, those two or three-position switches that are found on robot teaching pendants and in other applications to give the operator a way to stop machinery, even if they have already been injured or killed by the equipment. Calling these devices a ‘Deadman Switch’ or even a ‘Live-Man Switch’ as the three-position devices are sometimes called, sends entirely the wrong message to the user as far as I’m concerned. The objective of our work as machinery safety engineers is to prevent injuries from happening in the first place......”
  Reply With Quote
Old May 5th, 2021, 11:48 AM   #11
Manglemender
Member
United Kingdom

Manglemender is offline
 
Join Date: Jul 2007
Location: Lancashire
Posts: 1,198
Quote:
Originally Posted by dogleg43 View Post
Awww, evidently “deadman’s switch” isn’t appropriate any longer. From a 2011 article.
More years ago than I'm prepared to admit, I served my apprenticeship on the railways. Early electric trains had a "Dead Man's Handle" to control the speed of the train: Holding the handle at the correct height you could rotate it to alter the power (voltage) applied to the motor via a device called a tap changer. It was designed such that if the driver had a heart attack and died, even if he slumped forward onto the handle, the train would still stop.

I guess they are all consigned to museums now along with the travelling post office carriages that I used to maintain.

Nick
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Safety relay - working principle Dominic10 LIVE PLC Questions And Answers 13 February 19th, 2020 04:41 PM
Allen Bradley Guardmaster safety relay Low Voltage on S12 and S22 Baker in Virginia LIVE PLC Questions And Answers 1 April 23rd, 2017 01:39 AM
2-Hand Safety Relay with Latching baberb LIVE PLC Questions And Answers 2 April 8th, 2016 11:22 AM
Allen Bradley Minotaur Safety Relay jeb72 LIVE PLC Questions And Answers 5 March 11th, 2015 08:09 PM
MSR57P Speed Monitoring Safety Relay Mike Lewallen LIVE PLC Questions And Answers 0 July 9th, 2009 11:36 AM


All times are GMT -4. The time now is 09:21 AM.


.