Conductive electrical paste

Hi all,

i have this project in which we have to replace an AB 400 amp contactor used as the panel power contactor that is 20+ years old with a new one, had to buy a 460 amp one, all we could get on short notice. we will be pressure crimping 4/0 lugs to the 4/0 thin strand flex wire and use (2) cables per phase going to the contactor and from the contactor to the main power rail to avoid any corrosion issues, i suggested using conductive paste on the connections and the boss has agreed. i will place the paste onto the wire and then into the lug to be crimped.
Also, what about using this paste in rigid conduit fittings.

Any bad experiences or comments?

thanks in advance,
james
  Reply With Quote
Old June 9th, 2021, 09:09 PM   #2
sparkie
Lifetime Supporting Member
United States

sparkie is offline
 
Join Date: Nov 2014
Location: KS
Posts: 1,102
I honestly wouldn't put anti-oxidation compound inside of a crimp. I've never seen it done, and honestly don't have much of a need to. Crimps that big should be a cold-weld, or very close to it, and corrosion shouldn't be an issue. I see no problem using it for the connection to the lug or to coat the copper under the heat-shrink (if you are using heat shrink).


You would want to use copper antioxidant joint compound for something like this.


For rigid conduit fittings, use conductive anti-seize. Loctite Nickel and Copper both work very well for the purpose.
  Reply With Quote
Old June 9th, 2021, 09:11 PM   #3
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 548
I always use Anti-Ox in crimp terminals, also works for bolted connections.


Quick search found THIS brand, but others are available. Also sold at local electrical distributors, in the Detroit area at least.



Also works on car battery terminal wire connections.
  Reply With Quote
Old June 10th, 2021, 04:08 PM   #4
MikeyN
Lifetime Supporting Member
United States

MikeyN is offline
 
Join Date: Dec 2017
Location: Illinois
Posts: 128
Quote:
Originally Posted by sparkie View Post
I honestly wouldn't put anti-oxidation compound inside of a crimp. I've never seen it done
These are what we use in our plant, generally in the more corrosive areas. The anti-ox compound (they call theirs Penetrox) is prefilled in the connector and can also be purchased by the bottle.
__________________
C:\Dos
C:\Dos Run
Run Dos Run
  Reply With Quote
Old June 10th, 2021, 04:26 PM   #5
sparkie
Lifetime Supporting Member
United States

sparkie is offline
 
Join Date: Nov 2014
Location: KS
Posts: 1,102
For me, I just never see those larger connectors fail inside of a nice, tight crimp. I see connections fail on terminals / busses / lugs and at the exit of the crimp. To be fair here, I don't see any problem with using an antioxidation compound rated for copper connections inside of the crimp. I also don't have a clue if connections tend to fail like this in humid / saline parts of the country either.


It just isn't something I'm going to go out of my way to do unless specified.


One more thing I noticed. Make sure your antioxidation compound is rated for copper connections. The Penetrox linked to by MikeyN that comes in those connectors is a copper-rated de-ox, while the one linked to by I_Automation is only rated for Aluminum to Copper and Aluminum to Aluminum.

Last edited by sparkie; June 10th, 2021 at 04:36 PM.
  Reply With Quote
Old June 10th, 2021, 05:47 PM   #6
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,677
Antioxidant pastes aren't necessarily conductive, are they?

There are electrical assembly pastes that are specifically conductive.

https://www.mgchemicals.com/products...ssembly-paste/
__________________
  Reply With Quote
Old June 10th, 2021, 10:23 PM   #7
sparkie
Lifetime Supporting Member
United States

sparkie is offline
 
Join Date: Nov 2014
Location: KS
Posts: 1,102
Quote:
Originally Posted by Bit_Bucket_07 View Post
Antioxidant pastes aren't necessarily conductive, are they?

There are electrical assembly pastes that are specifically conductive.

https://www.mgchemicals.com/products...ssembly-paste/

Deox can be either conductive or a dielectric. I think most of the standard deox compounds like NoAlox and Deox brands have conductive additives, while anti-seize compounds for use in conduit joints pretty much have to be conductive.
  Reply With Quote
Old June 11th, 2021, 09:53 AM   #8
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 1,610
Here's what you are looking for
I used it years ago when I did costruction always kept a can on hand

http://www.tnb.com/ps/fulltilt/index...rt=CP8TB&co=US
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
OT: Consultants and Electrical Drawings Saffa LIVE PLC Questions And Answers 29 June 27th, 2020 01:49 PM
SolidWorks Electrical 3D allscott LIVE PLC Questions And Answers 7 August 15th, 2013 02:02 AM
Electrical Drawing Software Leeroy LIVE PLC Questions And Answers 19 May 10th, 2013 11:36 PM
AutoCAD for electrical schematics brendan.buchan LIVE PLC Questions And Answers 13 March 30th, 2011 11:44 PM
PID with an electrical heater??? RPax LIVE PLC Questions And Answers 9 July 7th, 2010 10:50 AM


All times are GMT -4. The time now is 12:34 AM.


.