Cooling a oven belt

Hello, I got a customer that has a shrink wrap machine to bundle up beer cans to make beer packs. They have a problem with the oven's all metal belt conveyor. When the belt gets too hot, the shrink wrap stinks on the belt and if the belt is too cold, the wrap doesn't shrink under the pack.


The machine has a big fan to cool the belt but it's manually operated with a potentiometer. If the operator notices that the wrap sticks, he turns the fan to a higher speed and if the wrap doesn't shrink under the pack, he turns the fan to a lower speed.



They would like to regulate/automate the belt temperature. A VFD will be installed.



I was thinking a simple PID temperature loop with the fan. A temperature probe would be installed after the fan. We would do some tests to figure out the optimal belt temperature in the oven versus the belt temperature after the fan.


Anwybody has a better idea how to achieve this?


Thanks!
Attached Images
File Type: png oven_belt.png (7.0 KB, 109 views)
  Reply With Quote
Old April 14th, 2021, 11:30 AM   #2
parky
Member
United Kingdom

parky is offline
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 3,233
You really need to test the temperature of the actual belt, this could be done with an infrared sensor, using a probe just above the belt is prone to problems, even if you allow for offset any slight air movement will probably change the reading and as direct contact is difficult with most sensors I would certainly look if a non contact method i.e. infrared with an analog output (if one exists) or the possibility of coms.
  Reply With Quote
Old April 14th, 2021, 11:34 AM   #3
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 10,986
Many years ago, I used one of these (before they were bought by Fluke):

https://www.flukeprocessinstruments....ers/compact-ci

There was also a little box of electronics that went with it which supplied a 4 to 20mA current output that was scalable to the measured temperature.
__________________
You've been taken, but you don't know it yet.
  Reply With Quote
Old April 14th, 2021, 11:38 AM   #4
goghie
Supporting Member
Serbia

goghie is offline
 
Join Date: Jan 2008
Location: Belgrade
Posts: 439
I would spray it with water instead cooling it with fan. Also you need to select good probe with fast response. Adding a photoelectric switch is also good choice, because you don't want to measure temperature on gaps. Infrared temperature sensors don't like reflective surfaces.
  Reply With Quote
Old April 14th, 2021, 11:50 AM   #5
TWS
Member
United States

TWS is offline
 
Join Date: Nov 2007
Location: virginia
Posts: 274
IR camera
  Reply With Quote
Old April 14th, 2021, 02:06 PM   #6
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 638
What I don't understand is that if the plastic should shrink and not stick inside the oven, why the temperature of the belt is regulated outside the oven?

Maybe the temperature of the lower part of the oven should be regulated separately from the upper part.
__________________
Suppanel HMI
  Reply With Quote
Old April 14th, 2021, 04:13 PM   #7
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 548
I would use Infrared thermocouples on the belt. I have used them to test panels with shiny Mylar laminated on them and there were accurate and reliable.

I would put one right after the fan area, if you want to tune the PID for it maybe add one right before the fan also in case the conveyor is warmer or cooler than normal going in .
  Reply With Quote
Old April 14th, 2021, 05:18 PM   #8
matwon
Member
Canada

matwon is offline
 
matwon's Avatar
 
Join Date: Mar 2014
Location: Québec
Posts: 15
Quote:
Originally Posted by lfe View Post
What I don't understand is that if the plastic should shrink and not stick inside the oven, why the temperature of the belt is regulated outside the oven?

Maybe the temperature of the lower part of the oven should be regulated separately from the upper part.

The belt is not currently temperature regulated, it passed through the oven heats up overtime.
  Reply With Quote
Old April 14th, 2021, 05:23 PM   #9
matwon
Member
Canada

matwon is offline
 
matwon's Avatar
 
Join Date: Mar 2014
Location: Québec
Posts: 15
I will check for infrared probes
  Reply With Quote
Old April 14th, 2021, 06:32 PM   #10
Mispeld
Member
United States

Mispeld is offline
 
Mispeld's Avatar
 
Join Date: Feb 2017
Location: VA
Posts: 549
Quote:
Originally Posted by matwon View Post
Hello, I got a customer...

They would like to regulate/automate the belt temperature. A VFD will be installed.
I realize the customer wants to automate temperature control, but the description sounds more like a measurement problem in that product quality is the feedback on whether the belt temperature is in an acceptable range.

Depending on circumstances and your relationship with the customer, you may consider a two-phased approach: (1) install belt temperature measurement with an operator feedback mechanism, and (2) add automatic control if human-in-the-loop is still not good enough.

As others pointed out, non-contact temperature sensing is probably the best option for measurement.

Operator feedback could be a visual indicator such as a three-color stack light (cold/good/hot) and/or a digital temperature readout. The operator would continue to use the existing potentiometer, but with advance information on temperature going out of range, they can make the manual adjustment before wrap quality deteriorates.

If this is good enough, you will avoid a lot of baggage associated with an automatic control that might be overkill for this situation.

But if the customer has already made up their mind, so be it. They are always right, you know.
__________________
"What a power grid is, well, it’s something different to everybody, and that’s what you gotta understand. I mean, would you rather have AC or would you rather have AOC?" -Blaire Erskine
  Reply With Quote
Old April 14th, 2021, 08:38 PM   #11
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 3,335
Quote:
Originally Posted by Mispeld View Post
I realize the customer wants to automate temperature control, but the description sounds more like a measurement problem in that product quality is the feedback on whether the belt temperature is in an acceptable range.

Depending on circumstances and your relationship with the customer, you may consider a two-phased approach: (1) install belt temperature measurement with an operator feedback mechanism, and (2) add automatic control if human-in-the-loop is still not good enough.

As others pointed out, non-contact temperature sensing is probably the best option for measurement.

Operator feedback could be a visual indicator such as a three-color stack light (cold/good/hot) and/or a digital temperature readout. The operator would continue to use the existing potentiometer, but with advance information on temperature going out of range, they can make the manual adjustment before wrap quality deteriorates.

If this is good enough, you will avoid a lot of baggage associated with an automatic control that might be overkill for this situation.

But if the customer has already made up their mind, so be it. They are always right, you know.
I think this is the best approach. At the moment you have no data to work with, and any attempt to control the process will just be speculative.

Install the measurement system first, along with visual feedback to the operator (like a temperature readout), then let them run it the same way they always do for a month or two. Any operator more advanced than a trained monkey is good at at least one thing: working out ways to make their job easier. I don't imagine that peeling stuck plastic off a hot belt, or re-wrapping pallets manually are fun tasks for them, so if you give them any sort of way to see those issues coming and circumvent them, I guarantee they'll get you the data you want. After a couple of months, go back and chat to them, and you'll likely get some really valuable information like "yeah, the plastic seems to start sticking as soon as the temperature goes above x°C so I start to wind the speed up as soon as I see it get to about y°. And then when it comes back down to z°C I back it off again before it stops shrinking the plastic." Basically, you're using the world's most powerful organic self-learning computer (the human brain) to gather the data you need, and then you've got a halfway decent shot of controlling the process, now that you actually know how you need to control it.

Or, as Mispeld says, you might find that the customer is happy with the manual control, now that they have the ability to foresee and prevent the issues before they occur.

From a sensor point of view, I've used the Raytek MI3 for non-contact temperature measurement with good results. My application was quite different, in that it was conducting product samples on surface temperatures as low as -40°C (or °F, that's the magic point where it doesn't matter which you use), and the sensing distance was only 20-30mm. But I'm sure there are other ranges. It's a good reliable sensor, had no problems with it after 7 or 8 years, and it's a nice easy 24VDC 4-20mA instrument.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Heating and cooling commands calculation g.mccormick LIVE PLC Questions And Answers 2 October 13th, 2016 02:23 PM
(PID fun) Unhealthy starts following belt type change cmothebean LIVE PLC Questions And Answers 2 January 7th, 2013 05:52 PM
Ignition system in industrial convenor oven syed misbah LIVE PLC Questions And Answers 5 March 28th, 2012 01:39 PM
Help with automatic belt tracking system - belt conveyor LJAM LIVE PLC Questions And Answers 8 October 3rd, 2006 04:41 PM
What is P in PID? ... Ron Beaufort LIVE PLC Questions And Answers 22 May 12th, 2005 06:29 PM


All times are GMT -4. The time now is 02:56 PM.


.