I'm thinking of using the ET200 ECO PN system on an upcoming project. What is there to consider when using this? It seems pretty straight forward, ethernet and power cable to the modules and just plug the M12 in and off you go. Can I use the same switch as I have between HMI and PLC?
/Tim
I have no experience with ET200 ECO but I am sure you can use the same switch as you use with the HMI and the PLC.
You might consider what topology is the smartest, so that if one device is down (i.e. the HMI) it does not affect the other parts (i.e. the PLC CPU or the IO).
If you have a star topology with the switch in the middle, it is simple since then only the switch is critical.
Dont use the cheapest switch you can find even if it is 'industrial' grade.
Minimum is an unmanaged switch from one of the big automation players.
I have used the ET200 eco pn input modules in few projects. They have been on use for ~2 years now no problems. Also we have used the Eco pn fail safe modules no problems yet.. Super easy to use and configure.
One of the big US automakers specifies ET200Pro controllers and I/O in their powertrain plants. Thousands of cards in operation now.
There is a VFD in that form factor, 1.1kW only. They have an IP65 switch in the same line, called SCALANCE XP.
I have no idea of the failure rate, the electricians don't seem to complain.
Hi I have a task to change a controlsystem on a plant. The existing PLC is a Siemens IM 151-8 with a profibus mastercard 6ES7-138-4HA00. My plan...
627
Hello, We have the following siemens DI Card 6DL1131-6BL00-OPH1 ( 32 channel) my question is in relation to the wiring of this card with the V50...
885
Hi, I have a question regarding the DI module 6DL1131-6BL00-0pH1, i am confusing myself with the family of IO, this is a 32 channel module. Can...
985
Hello, We have the following DI card that can accept 1,2 and 3 wire DI's ( 6DL1131-6BH00-0PH1). We plan on installing this card for use with a...
1,479
Hello, We have the following DI card that can accept 1,2 and 3 wire DI's ( 6DL1131-6BH00-0PH1). We plan on installing this card for use with...
1,907