PV550 612 No Active Nodes Found

John Simmonds

Member
Join Date
Jun 2008
Location
Tennessee
Posts
15
I'm trying to connect a PV550 (2711-T5A2L) to a 1761-NET-AIC using a 1747-C11 cable (w/RJ45 removed) and the Phoenix connector. Can someone tell me how to connect these. I though I knew but whatever I try results in 612. Thanks, John
 
@widelto: Years ago, I installed the PV550, 1761-NET-AIC and an ML1000 to a machine. Comm between the PV and the NET was via 1747-C11 cable with the RJ45 remove and a phoenix added. All was good until the PLC went bad - easy job (I thought) I'll just replace the 1000 with a 1200 but...
I tried Ken's suggestion but that didn't work either.
 
There are at least a dozen ML1000s on ebay for under $200; have you already spent enough time to justify one plus a few DOAs plus a few spares?
 
If you've replaced your "known bad" device and the connection you had before doesn't work.... then more than that device is bad or misconfigured.

Certainly it's possible the PanelView is damaged, or the 1761-NET-AIC or one or more of your cables.

But it's worth taking a look at the difference between a MicroLogix 1000 and a MicroLogix 1200 in this application.

The MicroLogix 1000 would "auto detect" DH485 traffic and switch into DH485 mode even if its serial was configured for DF1 Full Duplex.

On the MicroLogix 1200, you have to explicitly configure Channel 0 for DH485, and can still use DF1 for upload/download by pressing the DCOMM button.
 
Thank you for posting that followup !

While it is possible for DH485 to run at 9600 baud, it is so uncommon I have never seen it in 25 years of working with MicroLogix and SLC-500 controllers.

Glad to hear you got it working !
 

Similar Topics

Is there a way to add a stop to the attached program? I want to stop it after the first rinse so the operator would have to push a button for it...
Replies
10
Views
1,212
We have an old machine that has been mothballed since early 2018 and management are looking at more work for it in 2022. The system runs on an SLC...
Replies
12
Views
2,847
Trying to write a program for a PV550 (2711-T5A16L1, Ser. B, Rev. E, FRN 4.46) to test the touchscreen. I wrote a program with 16 pages and on...
Replies
2
Views
1,684
Good Morning Folks. Win Xp, PRO, Version 2002, SP3 RSLinx Classic 2.54 Using the AB UIC-485 driver with the 1747-UIC and a 2711-NC13 connected...
Replies
1
Views
1,212
I am converting an old Allen Bradley 550 to C-More. All is going fine But. is there way yo make a global object in C-More Like the the Old...
Replies
4
Views
1,929
Back
Top Bottom