compact logix not communicating with I/O

srv

Member
Join Date
Aug 2010
Location
QATAR
Posts
109
Hi,
i have a problem with my compact logix L35E controller.when i tried to download a program which was created in version 15.4,i updated the controller firmware to 15.4,but after downloading the program controller showing I/O communication error and processor going fault mode.can anybody help me.
 
Remember that CompactLogix controllers require an End Cap (1769-ECR) at the end of the I/O assembly, and that there are specific rules about how many modules you can connect before you need to use an expansion cable and another power supply.

You need to post details on the actual I/O modules and power supplies you are using, as well as details about the error codes you are seeing in the controller.
 
I am using 1769-L35E controller
slot
1 1769-SDN/B
2 1769-IQ16/A
3 1769-IQ16/A
4 1769-IQ16/A
5 1769-IQ16/A
6 1769-OB16/B
7 1769-IF8/A
8 1769-IF8/A
9 1769-IF8/A
10 1769-IF8/A
11 1769-OF8C/A

power supply(1769-PB4 series A) is in 3rd position from controller

when i am going run mode I/O status shows IO fault.(code 16#0010)mode or state of module does not allow oblect to perform requested service.

in controller properties window it is showing,"(Type 03) I/O fault,(code 23)at least one required connection not established before going in to run mode)

my 1769-SDN is in inhibit mode
 
Thank you for posting the followup information.

Those fault codes are consistent with a break in the 1769 I/O backplane connection or the absence of a 1769-ECR end cap.

Check each one of the 1769 bus connections to be sure that there are no bent pins and that the sliding bus connector is seated firmly and locked in place.

As I mentioned, CompactLogix requires the use of a 1769-ECR end cap attached to the rightmost module. The end cap contains termination electronics for the 1769 data bus.
 

Similar Topics

HI, Compact logix l32e controller is not communicating with Laptop computer (rslinx classic). The PLC is connected to an ethernet switch, from...
Replies
4
Views
2,193
I am having a problem with a compact logix L32E showing values on the display of a Panle View plus 1000. My graphics are all there on my touch...
Replies
7
Views
9,374
gents, I am trying to configure communication with EMERSON PK300 controller through port A1 using generic ethernet communication module . I could...
Replies
0
Views
93
I've blown the Output Transistor on the Output Card of a Compact Logix 1769-L24ER-QBFC1B It says J378. Does anyone know the replacement part...
Replies
3
Views
197
I am having trouble with getting no control of my analog output signal. I am using the SCL function block to control my analog output. The logic...
Replies
11
Views
240
Back
Top Bottom