Safety relay (Emergency stop) is designed in such a way that any faults in the input circuit are detected, e.g. contact welding on an emergency stop pushbutton or on one of the safety contacts on the output relay.

How it's possible to differ normaly closed contact from welded contact?
On which way Safety relays "feels" this difference? :confused:
 
Safety relay (Emergency stop) is designed in such a way that any faults in the input circuit are detected, e.g. contact welding on an emergency stop pushbutton or on one of the safety contacts on the output relay.

How it's possible to differ normaly closed contact from welded contact?
On which way Safety relays "feels" this difference? :confused:

Redundancy. The timing of the changes of states of redundant pairs of contacts must be within a very tight tolerance to be considered free of fault. It is highly unlikely that a contact will weld on a push button carrying very little current, but if one contact does become mechanically "stuck closed" it is also highly unlikely that the other contact on that same switch will also fail at the same time. The safety relay will then detect that one input string changed states and the other did not, regard that as a fault, and disable its outputs.
 
Generally E-Stop circuits are n/c, so you mechanically separate them, so they can't weld shut.

The biggest danger is the contacts fall off the mushroom and nobody notices until they need to operate it.
 
The biggest danger is the contacts fall off the mushroom and nobody notices until they need to operate it.


This is why the US automotive industry requires an extra contact that essentially reads true when the estop is correctly assembled.


Everywhere else, the best practice is to check all safety circuits once a shift/day/week to attempt to detect these sorts of faults.
 
Generally E-Stop circuits are n/c, so you mechanically separate them, so they can't weld shut.

The biggest danger is the contacts fall off the mushroom and nobody notices until they need to operate it.

I always use a self monitoring block

F5118364-01.jpg
 
As mentioned, dual redundancy and timing are how you tell if a contact is 'welded' or forced closed.

Additionally, some safety systems use a pulse wave to tell if all items in the circuit are 'ok'.
 
janner_10 said:
The biggest danger is the contacts fall off the mushroom and nobody notices until they need to operate it.
I see this scenario only of the E-stop is the kind that is placed in an enclosure that has room enough so that the contacts may not always be held in place.
In the self-contained boxes with E-stops that are usually placed in the field, the design is such that everything is either in place, or is so much damaged or wrongly assembled that you instantly can see it from the outside.

I always use a self monitoring block

F5118364-01.jpg
How does that work ?
If the mushroom is not mechanically connected to the contacts, does the contact switch over by means of an internal spring force, or ... ?
Am genuinely interested. Could be something we can use.
 
Redundancy. The timing of the changes of states of redundant pairs of contacts must be within a very tight tolerance to be considered free of fault. It is highly unlikely that a contact will weld on a push button carrying very little current, but if one contact does become mechanically "stuck closed" it is also highly unlikely that the other contact on that same switch will also fail at the same time. The safety relay will then detect that one input string changed states and the other did not, regard that as a fault, and disable its outputs.


Thanks for your reply, but I still can't imagine how it's possible. If we have NC EMstop button and if we press it, in the case when the contacts are welded there will be no opening of the contacts. So, in such situation how the safety relay will now that something is wrong?
Ohhh...in the case when both NC contact are welded, the relay can not "feel it"?
 
Last edited:
You have 2 of them (redundancy). Could be in an antivalent setup (NO+NC). The likelihood of them both welding is low. If you monitor the discrepancy time between them you'll know if something's wrong.
 
How does that work ?
If the mushroom is not mechanically connected to the contacts, does the contact switch over by means of an internal spring force, or ... ?
Am genuinely interested. Could be something we can use.
Jesper, those "self-monitoring" NC contacts are held closed only when they are mounted to the mushroom. If they fall off OR if the button is pressed, the internal spring forces the contacts open.
 
Jesper, those "self-monitoring" NC contacts are held closed only when they are mounted to the mushroom. If they fall off OR if the button is pressed, the internal spring forces the contacts open.

Exactly. It is like a 3-position switch.

It 'makes' in the middle when attached to a button, and unattached it breaks and pushed-in it breaks.

The only issue is that I have had some flake out and read open when attached. It is still safer than direct contacts, however, and those instances have been few and far between.
 
Thanks for your reply, but I still can't imagine how it's possible. If we have NC EMstop button and if we press it, in the case when the contacts are welded there will be no opening of the contacts. So, in such situation how the safety relay will now that something is wrong?
Ohhh...in the case when both NC contact are welded, the relay can not "feel it"?
You're correct if both sets of NC contacts weld, it won't work. But what is the probably of both them becoming welded at the same time?

The idea of a safety relay or safety switch is that while a contact may weld, it can be detected when the switch or relay is used by comparing it to the second contact. So, on the first failure it must be replaced.

This is also why there is a testing requirement on switches and relays as well. If a switch or relay is not normally used it must be tested at certain intervals (determined by the safety requirements) to see if one contact has welded (or has another failure). This reduces the likelihood of having two undetected failures before the next demand.
 
How does that work ?
If the mushroom is not mechanically connected to the contacts, does the contact switch over by means of an internal spring force, or ... ?
Am genuinely interested. Could be something we can use.
We use these almost exclusively, because the safety validations we have done on most clients require them. Essentially, we need to be able to detect that the contact block has fallen off the back of the pushbutton head, or else the e/stop looks just fine from the outside but doesn't work. That reduces your diagnostic coverage significantly, because a failure like that doesn't just take out one channel and get detected next time someone tries to use the e/stop, like a welded contact might, it prevents the safety function from working and the fault from being detected.

They work similarly to a lanyard - on a safety lanyard, the contacts are only closed if there's exactly the right amount of tension on the rope. Too much (rope pulled) and they open, too little (rope broken) and they open.

In the out-of-the-box state, the contact is open. The little yellow "fingers" on the contact block are taller than the fingers on all the other pushbutton contacts, so when you put them on the back of an e/stop, they get partially depressed and close. If you press them further in again, they open again.
 

Similar Topics

Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
Replies
1
Views
106
I have an application where I want to use a safety relay in combination with a flame detector as the sensing element. The flame detector has relay...
Replies
23
Views
1,076
I want to improve a semi custom product I am delivering to a customer with implementation of safety relays. The system is fairly simple with just...
Replies
5
Views
583
Hello, all, I am new here and pretty new to PLC'S. Closest thing I have to PLC experience is with avionics. At my new job I am a welding engineer...
Replies
4
Views
787
Back
Top Bottom