Question Message block between SLC and Controllogix

Hi All

Have any one sent a message block from a SLC 5/05 to a Controllogix L61 or similar Logix processor?
I need to get data from a SLC 5/05 to a Controllogix 5000 PLC over Ethernet preferable. I have a GSM module that slots into a Controllogix rack and I can generate sms'e from the proccessor and send it then out to clients giving critical process information.

Thanks a lot.
  Reply With Quote
Old July 9th, 2008, 10:05 AM   #2
widelto
Member
Colombia

widelto is offline
 
widelto's Avatar
 
Join Date: Jul 2005
Location: Barranquilla, Colombia
Posts: 3,022
Here you have three pics with my example in this case the 5/05 is telling the compactlogix that one of the tanks is open.

The language is spanish but i hope you can understand it.

Please let me know if you need more assistance.
Attached Files
File Type: zip message.zip (386.1 KB, 327 views)
__________________
My two cents.
  Reply With Quote
Old July 9th, 2008, 06:32 PM   #3
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 5,294
In preference, I would get the ControlLogix to READ the data from the SLC, together with basic SLC Status info, (like RUN mode, etc.)

Your CLX "SLC Data-Table Read" message configures easily, and there will be no need for "mapping" the SLC data-table file in the CLX.

(Mapping would be needed if the SLC wrote the data to the CLX, because the SLC has no means to specify a CLX tag-name, only another SLC-style data-table address).
  Reply With Quote
Old July 9th, 2008, 09:07 PM   #4
swhitlock
Member
Canada

swhitlock is offline
 
Join Date: Jul 2008
Location: Ontario
Posts: 5
Book Take a look at this technical tip from Rockwell

Rockwell has a decent technical tip on how to message between a ControlLogix and a MicroLogix (applies to a SLC as well). Take a look at this page. It explains both how to message from the MicroLogix to the ControlLogix and the reverse.

Notice, as Daba says, it's simpler to put both the read and write message in the ControlLogix so you don't have to setup mappings.
__________________
Scott Whitlock
PLC Programming Articles: http://contactandcoil.com/

Last edited by swhitlock; July 9th, 2008 at 09:11 PM. Reason: Add icon
  Reply With Quote
Old July 10th, 2008, 03:49 AM   #5
Hilgard
Member
South Africa

Hilgard is offline
 
Join Date: Jan 2008
Location: Rustenburg
Posts: 16
Thanks a lot you guys. I got it working!!!
Special thanks to Swhitlock the page you mentioned was the answer I was looking for.

Thanks.
  Reply With Quote
Old October 26th, 2017, 07:15 AM   #6
Latzi
Lifetime Supporting Member
Australia

Latzi is offline
 
Latzi's Avatar
 
Join Date: Nov 2007
Location: Brisbane
Posts: 118
Quote:
Originally Posted by daba View Post
In preference, I would get the ControlLogix to READ the data from the SLC, together with basic SLC Status info, (like RUN mode, etc.)

Your CLX "SLC Data-Table Read" message configures easily, and there will be no need for "mapping" the SLC data-table file in the CLX.

(Mapping would be needed if the SLC wrote the data to the CLX, because the SLC has no means to specify a CLX tag-name, only another SLC-style data-table address).
Problem with this is that if you are looking for an event t happen in the SLC to update some values in the CLogix you'll have to poll the SLC constantly so as the even is read right when it happens. Which will "put pressure" on the ethernet network. In this case I'd write from the SLC to CLogix only when the event is triggered.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
SLC 5/05 in ControlLogix I/O Tree? recondaddy LIVE PLC Questions And Answers 8 August 28th, 2020 12:37 PM
AB ControlLogix vs SLC? PaulKraemer LIVE PLC Questions And Answers 14 April 27th, 2011 02:41 PM
SLC 5/04 controllogix communication pct_jimmy LIVE PLC Questions And Answers 3 June 18th, 2008 11:11 AM
Need to move an AB SLC 5/05 processor programming to the new ControlLogix 1756-L55 piscis LIVE PLC Questions And Answers 2 June 14th, 2007 06:12 AM
SLC vs ControlLogix rsdoran LIVE PLC Questions And Answers 15 January 29th, 2003 11:39 PM


All times are GMT -4. The time now is 02:59 PM.


.