using the GREATER THAN command
Mas01
Oct 2020
Leicester, England
1,105
Is it possible to compare a D value to a K (decimal) value?
e.g. D300 is the water temp. I want to set M11 (lamp) to TRUE when it is greater than 25 Celsius. Or does the K250 also need to be a D value in order for the greater-than to work?
|--[> K250 D300]----------------------------(M11)-|
It looks like you are using Mitsubishi? If so, you can do a comparison like you want. As I recall, you need to swap the K250 and D300 in order to check if D300 is greater than 250.
well according to divine knowledge you first tell in which plc you want this ? and also comparing is done via registers and mov commands mostly ...
Yes, sorry, I should have said. It is indeed Mitsubishi. Thanks.
Ah yes, they should be the other way round, thus:
|--[> D300 K250 ]----------------------------(M11)-|
I know a little more of what I think you are trying to achieve, so at a stab I think you want to put a bit on when the temperature rises above a certain value to drive some pump or other equipment then turn it off when it gets below a certain temperature, correct me if I'm wrong.
-----[> Dxxx K225]------------(SET) // This is your bit so set it when above temperature
-----[ < Dxxx K100]------------(RST) //This resets the bit when it drops below a temperature
If your upper limit is say 22.5 (255) then the bit is on however, as soon as it drops to 22.4 the bit will go off and you will have the pump/control hunting
so you have two limits set the bit on the high limit 22.5 and reset it on 10.0 that way it will not hunt i.e. keep turning the equipment on/off
So you can set your limits of upper & lower temperatures.
Thanks. It's the other way round actually...I want to set an alarm (lamp) and turn an equipment off when the water gets too hot. But I guess the principles of.your code is still applicable. Many thanks.
On another note, is it possible to directly drive a lamp From an X input parameter eg X201 which is coming into the PLC on a QX10 digital input module?
Mas01,
I'm reading your posts on this forum and massive help you obtained from Parky, and I think that you owe him at least good lunch and couple of beers. :)
I hope that you know how much cost Mitsubishi support in UK.
The inputs only draw a few milliamps so it will depend on what feeds it, so for example a proximity switch to an input probably be capable of driving 100ma so providing what ever is driving the input is capable of say 5ma plus the current required to illuminate the bulb then yes there should be no problem.
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
45
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
156
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
48
93
90