Hi,

I have several Yaskawa V1000 VFDs connected via Serial Modbus to Opto22 serial modules. Everything is sort of working. I was able to set frequency references, start and stop motors, etc.

What I would like to do is to read VFD parameters. The manual "SIEP C710606 18F YASKAWA AC Drive – V1000 Technical Manual", Appendix C, states parameters can be read and written, under C.6, "Observing Drive Operations". However I am unable to find how to request the value of a particular parameter.

Any help will be appreciated. Thank you
 
I have not done this yet but very soon on Yaskawa E7 drive. I reviewed the manual. Your manual has very detailed specifics.

Look at V1000 manual page C-9 shows this

from what I found in manual you do the modbus read function code 03H, you can read multiple registers but they have to be consecutive. the data content in registers is separated into 8 higher bits and 8 lower bits for each register.

command message must include:
slave address: example 02H
function code:03H
start address
quantity
crc-16
 
Thank you AkaHammer, you are right and I am already reading data from the VFDs such as "Drive Status 1" (0020H) and Output Current (0026H). What I don't know is how to read parameters. For instance, parameter H5-02 (Communication Speed Selection), where is it? What register is in? Or how do I ask the VFD to "send" me the value for that parameter?
 

Similar Topics

I have an application where I have a 5HP TEFC Baldor running open loop from a Yaskawa V1000 drive. At times due to environmental changes the motor...
Replies
18
Views
10,015
Problem 1: I have the two wired up as shown below. ( Dip switch 2 is set to on on the VFD) Serial connections: Micro820 > V1000 D- > R- and S- D+...
Replies
15
Views
10,431
Using Yaskawa V1000 to drive a 2ft conveyor with has 1HP motor and motor rated current at 1.83A. I am running the conveyor the whole day, after...
Replies
13
Views
6,590
I'm getting ready to do a lab on communicating directly from an Automation Direct HMI to a Yaskawa V1000 using Modbus RTU. Surprisingly, I've...
Replies
4
Views
3,054
Dear Superiors,📚:wizard: I'm new for s7-300 and yaskawa v1000 drives communication via profibus. My aim is to find how to run the drive or...
Replies
1
Views
1,740
Back
Top Bottom