Panelview Plus-What is the best way to get back into Config Mode ?

Join Date
Aug 2016
Location
Virginia
Posts
343
Good Evening ,


I have a Panelview Plus that I need to go back into Config Mode. I understand that if you have a USB keyboard you can press the Default button and go into a screen that will allow you to go into config mode . Is that safe and easy to do ?


At one time wasn't there a white box you could press on bootup ?


Thanks so much for your help.
 
Many versions have the white square at bootup. I'm not sure which version first introduced it. Then there was one minor revision (somewhere around v6, IIRC) where they removed it, and following an immediate uproar, reintroduced it in the next minor revision.

Next bet is a USB keyboard and Ctrl+Alt+Shift+Windows

There are other ways in as well, but 99% of the time, those two will get you by.
 
I understand you can go to config mode using a USB keyboard.

But in my opinion, the best thing to do is put a 'Go to Config Mode' button in one of your screen, maybe with password protected.

But I guess now you have to upload the runtime file, add in the above button and download it back.
 
Can you connect to the PanelView with a VNC client? Use the "Send Ctrl-Alt-Del" button will cause the Windows CE OS to bring up the standard dialog box with the Restart Windows option. Win CE will restart to the desktop and when you start the PanelView Plus runtime it will go into config mode instead of running the application. At least, that's my experience with PV Plus 7 Performance.

Mike
 
The best way would be to put a go to configure screen button in your HMI program, either hidden behind something that would never be touched or locked behind a login screen.


If you forgot to do this and the little white square isn't there on reboots. Then you will need to either reset the panel view with the buttons on the back or plug a keyboard in and press Shift-Ctrl-Windows-Alt all at the same time until the end program screen pops up.



The keyboard method takes a few tries but it usually works.
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
25
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
46
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
72
Hello everyone. This is more of an HMI issue. I have a new PanelView Plus 7 Series B. I am using the alarm list object to display the fault...
Replies
0
Views
87
Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
125
Back
Top Bottom