PanelView700 Fatal 3B

descaldec

Member
Join Date
Jul 2012
Location
Dundas
Posts
3
Panelview Plus 700/2711P-RDK7C/Logic Module 2711P-RP8D/Factory Talk View Studio 12.00.00/Windows10. Ethernet.
I bought a brand new PVP700 display unit. I attached the old Logic board and message appeared FATAL 3B. Docs determine this is a firmware upgrade needed. I downloaded file to PC ok. Cant hookup to the display using ethernet. I know the IP address is 192.168.9.255 from cmdprmpt arp-a. I can see the panel in runtime target panel. Using firmware upgrade facility just wont connect to terminal
 
Hmmm, 169.254. is the prefix Windows uses when it fails to get IP settings via DHCP, IIRC.


Unless the host that is trying to connect to the PanelView also has an IP address on the 169.254.0.0/16 network, it cannot connect.
 
Give your pc a IPv4 address, if you think that the HMI is in the 192.168.10.x, give your laptop the address 192.168.10.254, usually with all PLCs and HMIs you need to give your PC/laptop a static address.
 

Similar Topics

Hello, I was trying to find the model no. for communication cables from Allen Bradley and was not able to find that. Can anyone please help me...
Replies
2
Views
4,689
Hi All, I've been pulling my hair out trying to fix this for a few days and need some advice. I have V19.01, v20.05, V21, V24, V30, V31, V32...
Replies
5
Views
350
Hello, this is my first post after being a long time creeper on this forum. I am experiencing a fatal error any time I attempt to print to PDF...
Replies
2
Views
357
Howdy Everyone, So recently I started getting a fatal error anytime I open the monitor in a specific program in logix designer error 0x800420b1...
Replies
2
Views
1,112
Hi all, I am getting a Fatal Error of 0xc0000005(-1073741819) While installing V21.03 on Computer(please refer to the attachment ) please help
Replies
5
Views
1,718
Back
Top Bottom