Load cell monitoring

We have a web converting process that involves the web passing over rollers with load cells on each end. This provides a tension readout from an amplifier into the PLC as an analog input. This signal is the sum of the individual load cell inputs.
Is there a way to monitor each individual load cell signal before going into the amplifier? We would like to know the individual signals while running with out upsetting the process.


Any ideas?
Thank you.
  Reply With Quote
Old June 10th, 2021, 10:13 AM   #2
AustralIan
Member
Germany

AustralIan is offline
 
Join Date: Jan 2013
Location: Leipzig, Germany
Posts: 1,240
You need a digital transmitter like the Laumas TLB4. This would send all four load cell values as well as the summed value to the PLC via your favourite comms protocol.


At one time we were using an Applied weighing AW190 intelligent junction box. Maybe this would be useful as a retrofit.
  Reply With Quote
Old June 10th, 2021, 10:14 AM   #3
busarider29
Lifetime Supporting Member
United States

busarider29 is offline
 
Join Date: Aug 2013
Location: Midland, MI
Posts: 166
Quote:
Originally Posted by Jim G. View Post
We have a web converting process that involves the web passing over rollers with load cells on each end. This provides a tension readout from an amplifier into the PLC as an analog input. This signal is the sum of the individual load cell inputs.
Is there a way to monitor each individual load cell signal before going into the amplifier? We would like to know the individual signals while running with out upsetting the process.


Any ideas?
Thank you.
Signal splitters? That would give you two outputs per load cell. One for your process and the other for monitoring. It's just one option. Could get expensive if you have a bunch of load cells. Just one option here

Last edited by busarider29; June 10th, 2021 at 10:23 AM.
  Reply With Quote
Old June 10th, 2021, 02:08 PM   #4
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: United Welfare States of America
Posts: 7,443
Quote:
Originally Posted by Jim G. View Post
Is there a way to monitor each individual load cell signal before going into the amplifier? We would like to know the individual signals while running with out upsetting the process.
It can be done but not without a lot of work. Load cells usually have outputs in the range of millivolts. The amplifiers have very high gain and amplify the output to a range of 0 to 10 volts. Gains of 2000 are common.


The problem is can you design of find other amplifiers with the same kind of noise free high gain and connect them so no noise is getting induced. It would be much easier to look at the amplified signals in the 0 to 10 volt range.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old June 10th, 2021, 02:43 PM   #5
busarider29
Lifetime Supporting Member
United States

busarider29 is offline
 
Join Date: Aug 2013
Location: Midland, MI
Posts: 166
Quote:
Originally Posted by Peter Nachtwey View Post
The problem is can you design of find other amplifiers with the same kind of noise free high gain and connect them so no noise is getting induced. It would be much easier to look at the amplified signals in the 0 to 10 volt range.
Just one of a few reasons I did away with all of our load cell amplifiers, and instead bring the load cell/s directly into a load cell terminal on the PLC.
  Reply With Quote
Old June 15th, 2021, 06:03 PM   #6
kamenges
Member
United States

kamenges is offline
 
kamenges's Avatar
 
Join Date: Nov 2002
Location: Brillion, WI
Posts: 4,190
Whose load cells are you using? Not that it matters much. Most of the bigger players in the web tension game will have at least one amplifier n the stable that will provide left, right and summed outputs. If not, PM me. I would have a couple of options.

Full disclosure, I am part of an organization that manufactures web tension control products.

Keith
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Weighing system, load cell transmitter scaling for PLC coco243 LIVE PLC Questions And Answers 29 May 5th, 2020 11:37 AM
SARTORIUS Load cell can't measure the weight of HF RockyNivas LIVE PLC Questions And Answers 2 December 12th, 2019 08:39 PM