power wire size for 10hp motor

Hi everyone !

A multiconductor wire 4x2,5mm2 would be ok ?

Normally a 10hp - 400V motor would pull 16-17A

A 4x2,5mm2 wire could carry around 21-22A according to many manufacturers,

Considering the wire will be on open strays, at open space and next to other small conductors, length of 30m max.

I know a wire of 4x4mm2 would be better,

But would 4x2,5 be a problem ?

The cable is copper and PVC

Thanks!

Last edited by joaco1993; June 10th, 2021 at 07:18 PM.
  Reply With Quote
Old June 10th, 2021, 07:04 PM   #2
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: Montgomery, AL
Posts: 635
I don't know the specs off the top of my head, but usually the mfg of any motor would recommend power cable size in their manual, no? Some would even sell the correct cable to use?
  Reply With Quote
Old June 11th, 2021, 06:24 AM   #3
saultgeorge
Lifetime Supporting Member
United States

saultgeorge is offline
 
saultgeorge's Avatar
 
Join Date: Jul 2015
Location: Detroit
Posts: 405
Hi, good morning!

Section 430 of the NEC covers motors. There are tables for FLA, types of motors and references to other tables for the correct conductor size based on the parameters I listed above.
It may also be that you're installing AC power cables in a tray that has analog and 24 VDC. There are many considerations to take into account when one mixes cable types and voltages. Hope this helps.
__________________
"Instant success teaches one nothing. Failure teaches one everything one needs to succeed."
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Allen Bradley 1769-L18ER-BB1B local 1734 point IO modules arrangements anirudhgk7 LIVE PLC Questions And Answers 11 November 11th, 2019 01:51 PM
Signal wire with power wire theripley LIVE PLC Questions And Answers 3 October 27th, 2019 09:49 AM
VFD doesn't trip on over current. rQx LIVE PLC Questions And Answers 22 March 17th, 2015 04:52 AM
Motor HP gain by reconnect? Dick DV attn leitmotif LIVE PLC Questions And Answers 14 August 22nd, 2009 07:52 AM
60Hz power for a 50Hz Motor Grover LIVE PLC Questions And Answers 8 November 27th, 2002 11:08 AM


All times are GMT -4. The time now is 12:45 AM.


.