plc storereviewsdownloads
Reply
Thread Tools Display Modes
Old June 10th, 2021, 07:42 PM   #1
dnlerwin
United States
dnlerwin is offline
How do I search for a particular instruction in Studio 5000
I usually do production support and I am the guy that comes behind someone else's program and try and debug.Often I see code that looks like this. Sequence routine
EQU(0,Sequence)------do something--------MOV(10,Sequence)
EQU(10,Sequence)------do something--------MOV(20,Sequence)
EQU(20,Sequence)------do something--------MOV(30,Sequence)
EQU(30,Sequence)------do something--------MOV(0,Sequence)
its great
But they often have in some other routine somewhere an instruction like
----Oh yeah if this happens----------MOV(0,Sequence)
So I want to be able to search for "MOV(0,Sequence)"specifically. If i search for Search for "Sequence" it returns to many results.
Old June 11th, 2021, 12:35 PM   #2
Operaghost
United States
Operaghost is offline
Operaghost's Avatar
Right-click on a tag and select Cross Reference. This only shows where that tag is used in logic as opposed to all the documentation that might use that word.
In the Cross Reference results, look at the field that says "destructive" if it says "Y" then that instruction affects that tag. Turns it on/off or changes its value. If it says "N" then that instruction looks at that tag but doesn't affect it. We are almost always looking for the destructive ("Y") usage.
OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar
Old June 11th, 2021, 12:55 PM   #3
drbitboy
United States
drbitboy is offline
drbitboy's Avatar
can you save the program as a pdf? then a regular string search would work e.g. [Control-F](0,Sequence or [Control-F](0,[space]sequence.
__________________
i) Take care of the bits, and the bytes will take care of themselves.
ii) There is no software problem that cannot be solved with another layer of indirection.
Old June 11th, 2021, 02:02 PM   #4
Operaghost
United States
Operaghost's Avatar
By default, the Logix 5000 software doesn't allow searching for instruction types using there three letter codes. But it can. And you can combine the instruction type with a tag name.
  1. Go to Search and select Find
  2. Click the Find Within button
  3. Under Components on the left, select Ladder Diagrams
  4. In the Options field on the right select Instructions
  5. Type the three letter code (ie MOV) then a space followed by your tag name
Something like MOV Sequencer (it is not case-sensitive)
You can type a partial tag name if you wish. But the order must be: instruction three letter code, space, tag name. I don't think you could search for two addresses though (MOV Sequencer CurrentState). I can't make that work.
The Find Within setting will be remembered in the future. You would only need to enable it once.
OG
__________________
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
RSLogix & Studio 5000 shazad5444 LIVE PLC Questions And Answers 5 October 27th, 2020 07:27 AM
Remote access to Studio 5000 Emulate controller - v32 radfahrer LIVE PLC Questions And Answers 2 October 31st, 2019 11:25 AM
Studio 5000 Find instruction help! Not working?? lunenburger LIVE PLC Questions And Answers 7 July 11th, 2019 03:25 PM
Studio 5000 Search Replace SophieA LIVE PLC Questions And Answers 8 August 29th, 2018 09:47 PM
RSLogix 5000 V15 Features Samneggs LIVE PLC Questions And Answers 18 April 20th, 2006 06:45 PM