Advice for connecting ground of RS 485 in PLC

Hi,

I am using a Kinco PLC (type: KT506-24DT) the PLC has a terminal for A & B connections of the RS 485 communication.

All these time I have been using a third ground line along with the A & B lines in my earlier circuits. The ground line would be connected to ground via 120 Ohm resistor on both ends.

My question is should I run a ground line along with the other two lines A & B of the RS 485 communication ? If so should this be connected straight to ground or via a 120 Ohm resistor as mentioned above ??

At present I have left the ground line open, and PLC is communicating very well with an Anybus gateway in a lab environment with a short RS 485 line, but I am not sure how its going to perform in an high noise environment.

Please advise on the best way of connecting the ground line ??


thanks
a
  Reply With Quote
Old October 9th, 2015, 11:51 AM   #2
nonuke
Member
Portugal

nonuke is offline
 
nonuke's Avatar
 
Join Date: Sep 2005
Location:
Posts: 840
Quote:
Originally Posted by arbj View Post
All these time I have been using a third ground line along with the A & B lines in my earlier circuits. The ground line would be connected to ground via 120 Ohm resistor on both ends.

My question is should I run a ground line along with the other two lines A & B of the RS 485 communication ? If so should this be connected straight to ground or via a 120 Ohm resistor as mentioned above ??

thanks
a
You don't need a ground line. You should use a crossed pair cable with screen. The 120 Ohm termination resistors should be connected between Data+ and Data- in the first and last RS485 module.
Search this forum for RS485 and you will find lots of information.
  Reply With Quote
Old October 9th, 2015, 08:12 PM   #3
gclshortt
Member
Canada

gclshortt is offline
 
gclshortt's Avatar
 
Join Date: Dec 2014
Location: Ontario
Posts: 3,187
Shielded Cable with Drain Wire
The drain wire is connected to the housing of the communication cable end connected to the PLC side of the cable. This will filter the ambient noise to one end. Connecting both ends will produce more noise on the cable.


Just some additional information. Hope it helps.
Garry
http://www.accautomation.ca
  Reply With Quote
Old October 10th, 2015, 10:57 AM   #4
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 3,191
Quote:
Originally Posted by arbj View Post
My question is should I run a ground line along with the other two lines A & B of the RS 485 communication?
RS-485 should have a signal ground wire, say all the people who deal with it:



The problem is that many vendors use the case/housing ground as the signal reference and over long distances, ground potential differences show up as a common mode voltage.



Those are the situations where common mode can become a problem and the only solution I know is to use an RS-485 isolator module.

I've seen 100 ohms used in a signal ground connection to earth ground, like in this Maxim App note 1137 (below), but that resistor should not be confused with the termination resistor needed to consume the energy of reflected waves at the transmission line end points.

  Reply With Quote
Old October 10th, 2015, 12:52 PM   #5
arbj
Member
India

arbj is offline
 
Join Date: May 2011
Location: mrt
Posts: 55
Quote:
RS-485 should have a signal ground wire, say all the people who deal with it:
Thanks for that information
  Reply With Quote
Old October 10th, 2015, 12:55 PM   #6
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,476
Some say yes some say no..see link

https://www.google.com/search?q=RS-4...m=122&ie=UTF-8
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old October 10th, 2015, 02:30 PM   #7
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 3,191
RS-485 works as long as the common mode stays within limits, as B&B points out:

"While a differential signal does not require a signal ground to communicate, the ground wire serves an important purpose. Over a distance of hundreds or thousands of feet there can be very significant differences in the voltage level of "ground."

"RS-485 networks can typically maintain correct data with a difference of -7 to +12 Volts. If the grounds differ more than that amount, data will be lost and often the port itself will be damaged. The function of the signal ground wire is to tie the signal ground of each of the nodes to one common ground. However, if the differences in signal grounds is too great, further attention is necessary. Optical isolation is the cure for this problem."

My experience mirrors that assessment. It always works the bench, it's when it gets distributed in the field that the problems start.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
RS 485 question 2rlp LIVE PLC Questions And Answers 6 August 7th, 2015 12:16 AM
Laser Coder and PLC Integration Advice Needed... JoseM LIVE PLC Questions And Answers 3 May 21st, 2012 08:17 AM
RS 485 Connections libbysen LIVE PLC Questions And Answers 1 September 26th, 2009 02:25 PM
Difference In Rs 232 And Rs 485 chauhanrasikendra LIVE PLC Questions And Answers 6 July 1st, 2005 09:08 PM
RS 485 Micrologix kirk LIVE PLC Questions And Answers 2 September 16th, 2003 03:09 PM


All times are GMT -4. The time now is 03:15 PM.


.