hi, so anyone know how to connect a haiwell HMI with XINJE PLC by using MODBUS communication protocol? please help me ASAP. thank you
 
You will be hard pressed to find anyone using either of those I am afraid. Good luck.
 
reply to BOB

hi BOB, thank you for the reply, have you ever worked with two different kinds of HMI and PLC where serial communication doesn't support.
 
Modbus Generalities

This is a general comment that is not specific to your situation.

A common mistake for someone implementing Modbus is not having some understanding of Modbus FIRST. This may mean studying the Modbus spec. Us older types have a printed 'Modicon Modbus Protocol Reference Guide' PI-MBUS-300 Rev J (1996). I'm sure the Modbus association people have an online equivalent. You need to have an understanding of the different function codes. There's about 24 of them - you can completely ignore the majority. Most work can be done with just 3 and 16. The next ones to understand are 1 and 15. 2, 4, 5, and 6 are the last place that most people need to go.

The PLC class outline at CorsairHMI.com has some Modbus material including some discussion of the 1-register address offset issue that seems to plague most first-time Modbus users. It also has some discussion of the double-integer and floating point considerations. There seems to be a lot of other (and better) available guides to the topic. Chipkin Automation Systems 'Modbus for Field Technicians' by Peter Chipkin is a good resource and much better than anything that I have written.

I'm sure that there are plenty of people that love or hate Modbus with valid reasons but it's not going away any time soon. It may outline us all.
 
As a basic consideration, the HMI is usually a Modbus master/client, for the sole reason that Modbus is a master/slave protocol and slaves are silent unless spoken to. If the state of a selector switch is changed on the HMI, it's up to the HMI, as a Modbus master, to write that change to the PLC.



If the PLC were the master it would have to continuously poll/read dozens/hundreds of status words looking for a state change on the HMI.
 
Basically

- You will have, in the PLC manuals, to learn how to configure Modbus and see which Modbus addresses correspond to the bits and registers that you want to manage on the HMI.

- You will have to make the physical connection between PLC and HMI. If it is Modbus RTU you will need to consult the manual of both and obtain or manufacture the appropriate serial cable. If it is Modbus TCP, both devices must be connected via ethernet on the same subnet and you must assign IP addresses.

- You will have to configure the HMI to connect as a master to the PLC and create the screens to display or modify the bits and registers Modbus addresses of the first point.
 
I have used Xinje PLCs but only with Xinje HMIs. The HMIs are pretty cheap and the software is free, it would be the easiest way forward.
 
hi, so anyone know how to connect a haiwell HMI with XINJE PLC by using MODBUS communication protocol? please help me ASAP. thank you
This is a very common problem, we would see this very frequently at Schneider Electric.

Modbus RTU or TCP? (or surprise the heck out of me and pick ASCII)

If it's going to be Modbus TCP (or whatever AdHMI supports), I would recommend getting the Free & Fantastic AdvancedHMI ("AdHMI") and using it as a "translator" or "go between" between the Haiwell and the XINJE. Once you get both sides talking the same dialect of Modbus you can remove the AdHMI "node".

The initial intent would be to have one network that consists of the PLC to AdHMI, and a second network of AdHMI to the HMI and let AdHMI pass the data (with any required modifications) between the two nodes.

This way you can debug each side without having to fix everything at once.

You also can do this using other free or commercial tools.
 

Similar Topics

Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
53
can i send and recieve data using my yokogawa UT35A controller with my siemens s7 1200 plc using profinet communication without using gsd file
Replies
1
Views
378
Hi hope all are ok. I have mitsubishi PLC Q03UDV CPU. I have control a drive through modbus inteligent module QJ71MT91 in GX Works2. Any experts...
Replies
1
Views
582
Hi all, Has anyone dealt with Modbus RTU communication using SE`s Machine Expert? I have got the modbus tcp working, but not used the serial...
Replies
1
Views
1,208
HELLO EVERY ONE I need help in i am trying to establish modbus communication between two vfd's and delta plc the problem is that only one vfd is...
Replies
0
Views
1,705
Back
Top Bottom